Min. concrete over radiant heat pex-al-pex (MLC) tubing

mercedes
mercedes Member Posts: 67
Finally layout the Foamular 250 foam board square cut but only can find tongue and groove boards. Now the slab is going to be 6". I brought rebar chairs 2.5" using #4 rebar my clearance to the top of the concrete is 1 1/4 ". I think this is to shallow. Thoughts?

Comments

  • mercedes
    mercedes Member Posts: 67
    Sorry the tubing will be 1 1/4" from the top of the concrete.
  • Zman
    Zman Member Posts: 7,610
    I think that will be perfect. Nice job.
    Check this out https://www.pmengineer.com/articles/92439-exploring-all-the-aspects-of-tubing-depth
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Rich_49
  • hot_rod
    hot_rod Member Posts: 23,059
    the concrete folks suggest 3 times the aggregate size over any tube, bar, etc. Most red mix plants use a 5/8 rock.

    In some 1-1/2" thin slabs we requested a 3/8 "pea gravel" mix. Smaller aggregate, lest strength, but for a residential floor not an issue.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mercedes
    mercedes Member Posts: 67
    Zman and hot rod

    Thank you for the advice and help. Here are some pictures of my radiant heat for my garage.
    The Pex-Al-Pex is dead center of the slab 3" (slab total height 6")
    Stego vapor barrier 15 mil (in yellow on the perimeter)
    2" Dow Tongue and groove foam boards (could not find sq edge w/o snap lines
    2 1/2" rebar chairs (18" on center) with # 4 rebar criss-cross
    Uponor pex rail tie to the lower rebar to hold the tubing in place
    Uponor Pex-AL-Pex tubing 1/2" 885' total
    Caleffi 4 port manifold 6686D5S1A with flow meters
    Caleffi Pex-Al-Pex adaptors for the manifold 6825400

    Thank you again
    Dan





  • mercedes
    mercedes Member Posts: 67

  • hot_rod
    hot_rod Member Posts: 23,059
    Looks nice. How much over the top of the upper rebar? You want a good inch or more to prevent “road map” cracking
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mercedes
    mercedes Member Posts: 67
    Hot rod

    I will have from 1 1/2 to 2" also in the spring I will have 1/2" stone tile on top. Thanks Dan
  • hot_rod
    hot_rod Member Posts: 23,059
    Great! A cleavage membrane or brush on product it a good idea to keep any slab cracking from telegraphing to the tile

    The Tile association websites have good info for that detail