we did a new steam boiler a while back, planned on coming back when the weather was cooler to do some good skimming. The people started the boiler before we could get back and noticed some strong odors in the radiator vents (one pipe). I went a skimmed, there seemed to be more oil than normal. Now they say it's better but still noticeable. Is there something i can add to make it smell better? I've never experienced this concern. Thanks
0
Comments
-
More skimming possibly wand washing the boiler, it will fade eventually. Washing WILL get though.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
I'm sorry i hav't done a wash, fill up the mains and drain it?0
-
The fastest way is to use a wand to wash off the oils
https://www.youtube.com/watch?v=q1tw9rz-pUk
The steam mains get steam cleaned every tome the boiler comes up to steam so the majority of oil smell is probably from the boiler itself. You could dump a half dozen steamaster tablets into the boiler and let it go crazy for 20-30 minutes, that will cause heavy foaming and should clean anything in the boiler risers and header.
Make sure you flush out the boiler good after this and fill it yp to the normal water line, you can then add one or two steamaster tablets to treat the boiler water for normal running.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
thanks Bob, i'll try some tablets 1st.
0 -
To be clear you have to bring the boiler up to steam for 20-30 minutes, there will be groaning and thumping during this time but ignore it. Then shut the boiler down and drain it all out, refill it up to the boiler takeoffs after it cools and drain it again to flush it out. I would repeat the flushing twice before filling it up for normal operation, then you can commence to skim.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge-1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements