Residential Hydronic System
Rubicone
Member Posts: 1
After flushing the float chamber and the system started up there was a repetitive clanking noise in the distribution pipes and one of the components (see attached photo) started to overheat to the point that the smoke alarm went off - although there was no visible smoke but a smell of sorts in the air. Only one of the radiators was receiving any heat. Does anyone here have any thoughts of what is happening and offer possible solutions?
0
Comments
-
I have to plead to you that I have never seen a circulator with a steam system if that is what you have.0
-
That's an electric side arm heater.
You probably don't have good flow through it which is causing it to overheat.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
As @Ironman correctly stated that is an electric heating element heating a hydronic (hot water) system. Before you energize this heating element:
Make sure the system is full of water and vented
make sure the circulator is running and moving water
Make sure all valves in the system are fully open
Failure to do this will cause a failure (burn out) of the electric element and you will have to replace it.
I don't know who made that heater, maybe Chromolox, or Warren Electric1 -
Is the pump working?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements