High Pressure Steam Level Control
Nashville_Hot_Water
Member Posts: 3
So I know this isn't really a forum for industrial applications, but thought I'd give it a shot anyway. I have an application with an indirect fired high pressure steam vessel. It is a u-tube shell and tube heat exchanger with hot oil in the tubes. They are making 920lb steam! Whoa..
I need some kind of level control to turn the feed water on and off.... and yes, they can weld on to the ASME vessel.
I know there are water tube boilers out there that operate in this range, how do they do it?
Thanks!
I need some kind of level control to turn the feed water on and off.... and yes, they can weld on to the ASME vessel.
I know there are water tube boilers out there that operate in this range, how do they do it?
Thanks!
0
Comments
-
If you call the Burnham Boiler Company I am sure that they can help you with your boiler and answer your questions.0
-
920 lb is way out of Burnham's speed and league.
You need to contact someone who sells HIGH Pressure steam specialties
1. SPX Copes Vulcan
2. Fisher Controls
3. Spirax Sarco
4. Armstrong
Goggle them and find an area rep. Don't screw around with a distributor
0 -
Sorry I ment the Hurst Boiler company from Coolidge, Georgia.
1877-994-87780 -
Thanks EBEBRATT-Ed! I'll check those out.
leonz, I have worked with Hurst Extensively in the past. They make good stuff, but even this pressure is out of their league...they max out at 450psi... I was thinking of Victory Energy. They make up to 2000 psi water tube boilers. With that said, any of these companies are sourcing controls from another manufacturer, just got to find the right controls manufacturer!
...also, a 2000psi boiler might scare me a little0 -
Level control is probably in a pressurized external vessel supplying your heat exchanger. Fortunately level control is not critical because the hot oil's temperature is controlled.What you have can be called an unfired boiler so perhaps that is what you should google.
In my day I don't think they sold thermal oil for such high temperatures. 500°+? I think a company called Ameritherm made molten salt boilers to power unfired boilers for such high temperatures.0 -
Check with Marsh instruments in Ohio0
-
Thanks for everyone's efforts! I ended up with Orion Instruments... Pretty cool stuff here!
orioninstruments.com
0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements