Piping 2-Pipe Steam Radiators
New England SteamWorks
Member Posts: 1,526
I have a project where I have to install some new (used) 2-pipe radiators in an old Dunham system with traps. The original existing radiators all have the inlet at the top (as normally seen), and the outlet mostly on the same side, but sometimes opposite side, at the bottom.
The replacement radiators do not have top inlets. Seems to me if I pipe the inlet at the bottom, the condensate will drain into the supply, rather than leave via the trap/return condensate line. But the customer states they have another two pipe building with traps where all the inlets are at the bottom. Thoughts?
The replacement radiators do not have top inlets. Seems to me if I pipe the inlet at the bottom, the condensate will drain into the supply, rather than leave via the trap/return condensate line. But the customer states they have another two pipe building with traps where all the inlets are at the bottom. Thoughts?
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
0
Comments
-
I've got bottom original supply-and-return tappings on a couple of buildings I service in NYC as well. Unless someone says otherwise, I'd not give it much thought. Give each radiator a pitch of 1/20 of an inch per foot toward the return and I'm sure you'll be fine.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes3 -
could also use a concentric reducer for inlet and eccentric reducer for outlet.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.1 -
Or eccentric on both, just at opposite positions. Though that probably costs more.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements