Lose of prime
pgrant89
Member Posts: 1
in Oil Heating
I was wondering if some one may be able to help me out with this problem I am having with an oil burner that as been giving me problems.
So it started last year there was a crack in the oil line it was buried in concrete so I had the guy replace the tank. I ran new oil line to it 3/8 coated line the old line I could never get a solid prime out of it this one I get a solid prime but after a couple of weeks it loses the prime it's a bucket cf1400 burner gravity fed the tank is close to 20' away
So it started last year there was a crack in the oil line it was buried in concrete so I had the guy replace the tank. I ran new oil line to it 3/8 coated line the old line I could never get a solid prime out of it this one I get a solid prime but after a couple of weeks it loses the prime it's a bucket cf1400 burner gravity fed the tank is close to 20' away
0
Comments
-
If it's losing it's prime you have a vacuum leak and/or possibly (but not likely) a bad pump. A vacuum leak could be anywhere in the fuel system from a bad seal at a flare fitting, bad seal at filter gasket and/or bad seal at the fuel pump cover.
Have the guy who replaced the tank and the oil line do a proper power bleed. He should also do a vacuum check on the fuel line and the fuel pump and check the pressure and cut-off for the fuel pump. Also check all fittings from the tank to the burner.
If he doesn't know how, doesn't believe in it, and/or doesn't have the right tools or skill, you should find someone else.
Hopefully when you replaced the tank you didn't dump the old oil into the new tank.There was an error rendering this rich post.
0 -
Gravity fed?To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
You should absolutely never loose prime if it is gravity fed.
Need pictures0 -
This is for your home? That's a big BTU burner.
One pipe oil line off the bottom of the tank?
Same level or higher than the burner?
If so, you'd have a visible oil leak.
Is the fuel pump the "B" or "H"?
The H pump needs an external (field installed) bypass line for low fire.
With the B pump, it's done internally.
When the high fire solenoid valve closes, and pressure drops from 300 psi, that extra oil needs to be returned to the inlet.
I don't think you have a loss of prime. I think there's a problem with the pump settings, piping, or adjustments.
Call a service company that has experience with commercial burners.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements