Amtrol water maker, 41 gallon model. 10 gallons and she's done.
older_dog
Member Posts: 8
New amtrol 41 gallon water maker. 10 gallons and it's cold. This has a mechanical aquastat and is heated by an HTP boiler. The aquastat does not seem to be functioning properly. My plan is to install the 10k ohm sensor and see if that works. Any ideas?
0
Comments
-
Is the aquastat new with the tank?
The aquastat is just switching? Not 24v powered with lights?
Is there a differential setting?
Heat loop air bound?
Dip tube installed?0 -
Zone valve or pump?Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0
-
pictures0
-
What was the previous DHW heating system and did it perform better?0
-
-
The
Yup agree pictures do a good job of cutting out long drawn out guessing posts....EBEBRATT-Ed said:pictures
0 -
Sorry, no pics yet. Update. I replaced the aquastat with the 10k ohm sensor. Nowi can read the temp of the tank from the boiler control panel. I poured heart to the tank and got that temp up to 123F. Got maybe 2 gallons of hot (nowhere near scalding) water into the tub. Basically the sensor is telling me i have a full tank of hot water but reality says basically no hot water. Controlled by pump. I'm guessing around but when the pump is running both supply and return lines get super hot.0
-
I meant I'm guessing airbound.0
-
@older_dog
Seems like the tank IS up to temp.
Are you sure the dip tube was installed?
Supply and return will get hot.0 -
I don't know what the dip tube is
.0 -
Dip tube0
-
Sure wish i knew what a dip tube was.0
-
Maybe you need to know that this is not a boiler mate it is a hydromax, all piped from the top.0
-
In the I&O manual, whether you have the BoilerMate or HydroMax, look at replacement parts.
The cold water dip tube brings the inlet cold near the bottom of the tank, ensuring you only draw hot out the top of the tank when needed.
If it's not there, the cold will just enter the top of the tank and get drawn right back out the hot side.0 -
Thanks. Don't understand why the unit wouldn't come with it already installed but i will check.0
-
It might be installed....should be in the cold inlet side.
Might the H & C connections be reversed?
If so you would be getting some hot water off of the bottom of the tank and with cold entering the top it would cool off the bottom as it fell by gravity.
On conventional WHs the dip tube is movable from port to port, don't know about your tank though.0 -
Wouldn't be the first time, but is easy enough to check -- the H & C connections should be labelled on the top of the tank. Draw hot water at a tap, and the H connection should be hot and the C connection cool or cold.JUGHNE said:...
Might the H & C connections be reversed?....
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements