Valve Repairs
Grallert
Member Posts: 743
I hope everyone is having a nice summer. While eleven of our radiators are off campus for a well deserved spa vacation I thought I would free up the valve and look into replacing the seats.I don't want to do any harm to these so I thought I'd ask the experts.Do any of you folks have experience servicing these. The system was installed in 1928 as a vacuum system and at some point a few years before I was born the vacuum pump was removed and the system was connected to two new boilers on a two pipe pressure return system upon completion of a large wing addition. I'm not sure it ever worked properly after that. Over the years the system pressure was bumped up to about 10psi causing issues that were covered up in the 90s with the very costly installation of a steam coil air handler. The eleven radiators on vacation are about a quarter of the radiators in this smallish auditorium. Anyway, can and should these valves be repaired?
Thanks for any advice, input etc. Sorry about the upside down pictures.
Peace
Matthew
Thanks for any advice, input etc. Sorry about the upside down pictures.
Peace
Matthew
Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker
0
Comments
-
Sarco and Hoffman --can't get much better than that. However, neither system was happy on pressures much over 1 psi. So the first thing to do is to make sure your system pressure is down where it belongs.
Then the question is what is the symptom that suggests repairs are needed?
Incidentally, I hope you kept track of which valve went with which radiator -- since the valve and the spud in the radiator are a matched pair, and can't be swapped around without a very good chance of leaks...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Yes I only removed two of the eleven so as I wouldn't forget where they live. The boilers are as low as I can get them with out lots of short cycling. about 2.5psi at that pressure these eleven radiators get very little heat through the one inch pipe. This is the reason ( I think) that the pressure was increased over the years between 1956 and two years ago when I started here. You see this section of building, built as a gymnasium was added on the our main building two years after the main was completed. That would be 1928. This gymnasium was heated with it's very own boiler and vacuum system. Long gone now but very clear on the original plans I have. 1956 saw a major addition and upgrade to the plant with the addition of the still operational Pacific Steel boilers and the removal of the plant running the system in the gym than library now auditorium. Oh I got a bit off track there but its good back ground. At the previous 10 to 12 psi operating pressure all these radiators got hot, over heated. The valve could not hold back that steam and I suspect it's because the seats are beat to heck. They sure look torn up. Also some of them simply no longer turn. I would like to, at a point in the future repair all the other issues Centennial Hall (that's what we call it now) has and return it back to a vacuum return system. That might be a pipe dream but, you know, it's worth thinking about.Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0
-
Where are you and this system located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
can a vacuum pump be put back in?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
We're in the Berkshires of western Mass. One of those Iconic boarding schools that look so picturesque when you drive up. The sausage is great just don't watch how it's made
I think maybe I can put a vacuum and a condensate pump at the end of the system once the piping is repaired. Luckily we have a backup with the air handler.gerry gill said:can a vacuum pump be put back in?
Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0 -
@Grallert -- there are a few of us who are in your area. Most notably @Charlie from wmass . Might be amusing to visit. We won't eat the sausage, thoiugh...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
One of my favorite things about this job is showing folks around. I'd more than happy to show you guys around. It's a neat place with a lot of history and has survived a lot knuckle heading and some pretty ingenious work arounds.Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements