Oil furnace. No power
hubbyho
Member Posts: 7
Hi guys.
I woke up to no hot water. I have a multi zone oil furnace with power to the controller and low water cutoff but no power to the aquastat or burner. Any suggestions as to why the aquastat wouldnt have 120v?
I woke up to no hot water. I have a multi zone oil furnace with power to the controller and low water cutoff but no power to the aquastat or burner. Any suggestions as to why the aquastat wouldnt have 120v?
0
Comments
-
Does power go from the LWCO directly to the aquastat? Is there power on the load side of the LWCO? Are you testing with a meter or just seeing status lights?0
-
Thx HVacNut.
Im seeing the lights on the Lwco but metering others. 110v (measured it) comes in and splices, one to the lwco and the otherbto the aquastat. Measuring L1and L2 of the aquastat has no voltage. I dont understand that. I have 0v at the TT 24v connection which i think is correct when calling for heat.
I double checked the burner and i do have 110v at the pigtail but no lights on the primary ignition controller.
Still stumped0 -
Are you measuring to neutral or to ground? An interruption on the neutral side can be tricky to find.0
-
-
Keep in mind that if the aquastat is calling for heat, you will have the same voltage on both sides. Also, not sure what you mean by the 110 coming in and splices? If all the controls are 110 except the thermostat, then they should all be on the hot side...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
It's likely the LWCO has failed, or the sensor needs to be cleaned. What model LWCO, and can you post a pic of its internal wiring? (Turn off power first)
Ok, wait, you DO have 110v at the primary? Then you should have 110v at B1,B2 on the aquastat unless the primary has seperate L1 and Limit terminals and powered independently.1 -
I have a safegard 1150 lwco and honeywell aquastat....0
-
Doesnt seem to want to upload pics.
To clarify for jamie, the hot comes in and is spliced to a red and black wire. Red feeds the lwco, the black to the burner.
Does the lwco provide power to the aquastat?0 -
Ive got three wires coming in to the lwco, neutral red n black. The black wire goes to the aquastat, red should be 110v and white neutral. Can i connect the red 110 tobthe black going tonthe aquastat to see if it powers on?? That would isolate the lwco as the culprit, no?0
-
Lwco0
-
-
-
Find the instruction for whichever Aquastat you have also. It will have in internal schematic.0
-
Thanks to everyone, especially HVACnut. I graduated a 900hr HVAC course in the early 90s and never put it to work in the field. I have enough confidence to tear into things but then find myself second guessing, relying on forums like this to get me to solutions. Thank you for the warnings and the push!
Turned out to be the lwco which i replaced in 2009. Thats not very good life expectancy! But thanks again for all your input!!!1 -
wow, someone actually came back to say thanks, impressive!!!"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements