creeping up boiler pressure
Comments
-
First shut off the automatic feed to the boiler. The prv may be leaking by. Try that first. If the pressure continues to rise with the water shut off you can disconnect the boiler mate coil plug 1 connection and test that. Or install two valves between the boiler mate and the boiler is probably a better idea2
-
Whoops, fill valve thing again...Leave it off at all times except for initial filling and stabilization, was my policy.....If fill valve is truly off and holding ,your issue is most likely the coil in the water tank....Careful how you describe it when looking for any manufacture warranty....Some warrant the tank for extended periods, but the coil is not....tricky tricky manufactures0
-
-
This is a common problem and one that has had me perplexed for years. Check the x-tank, replace the fill valve or somehow test the HX coil in the indirect. I can't tell you how many times everything has checked out fine, but the pressure continues to go up.
The latest one to add to the list is a bad Spirovent. For some reason, something in the Spirovent made the pressure go up.
There's magic in hydronics, but sometimes it's bad magic, no?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I just have to know, how does a spirovent cause the pressure to go up...This is a common problem and one that has had me perplexed for years. Check the x-tank, replace the fill valve or somehow test the HX coil in the indirect. I can't tell you how many times everything has checked out fine, but the pressure continues to go up.
The latest one to add to the list is a bad Spirovent. For some reason, something in the Spirovent made the pressure go up.
There's magic in hydronics, but sometimes it bad magic, no?1 -
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Read thru the posts, but still confused how a spiro vent can increase pressure...
0 -
The Spirovent's x-tank connection gets clogged. Seemingly (rarely) prone to Spirovents....8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
So it's not really really the spirovent causing the pressure to rise...because it's pretty much impossible0
-
I believe he means that the bottom port (1/2 npt tapping) on the spirovent got clogged with junk, thus not allowing the x-tank connected to it to do its job. However, this should cause the pressure to go up when hot (no place for the increased volume of water to go other than to press outward), then return to normal when cold. So something isn't being described accurately here.0
-
I agree totally if that's what's happening, but it was the wording that could be misleading. Spirovent causes pressure increase?zmcgarvey said:I believe he means that the bottom port (1/2 npt tapping) on the spirovent got clogged with junk, thus not allowing the x-tank connected to it to do its job. However, this should cause the pressure to go up when hot (no place for the increased volume of water to go other than to press outward), then return to normal when cold. So something isn't being described accurately here.
0 -
Give me that cheap cast iron air scoop and float bleeder any time ..
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements