boiler sizing

smokeygeo
smokeygeo Member Posts: 1
Hi,
My parents have a 2,200 sq ft house and a 300,000 btu/hr gross input steam boiler (weill mcclain). It's a monster. They said their contractor "just replaced the old one with the same size" 20 years ago. But heat never gets to the upstairs of their 2-pipe system.
It's hard to do a radiator sizing b/c most of their radiators are behind fixed cases but my guesstimate is 600 sq ft of steam compared to my house where I measured all the radiators using the on-line guides (and the 175,000 btu boiler does great w/ the 475 sq' of steam I have).They have a lot of big radiators.

Any suggestions for them?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,521
    Problem is almost certainly not the boiler. Make sure the pressure is limited low enough -- no more than 1.5 psi. Make sure all the traps are working (even one trap failed open can mess up a whole section of a heating system). Sounds obvious, but make sure there are no odd valves somewhere which are closed.

    Where are you? They might benefit from having the system gone over by a person who is a steam expert, and if you let us know where you are we just might know someone.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 17,314
    What Jamie said. This sounds like a Vapor system. You need someone who understands these grand old systems.