Dealing with chimney contractor
Absolute Mechanical Co. Inc.
The chart I have for multiple appliances into a flex liner suggests even an 8" at 45' would be sufficient. 10" sounds too big too.
14" 70' tall sounds insane.
Can you get a second opinion?--NBC0
Nfpa 54. Has great charts,,as well as manufactures of the flexi crap, provide the ratings....call the manufacture present him with the details and he may or may not help you...Definitly a mistake you don't want to go thru...Ultimitly, it's on the installer, he had best know his business, people hate it when they get c o poisoned...Now that's a bad day...Go by the book....0
The boiler manufacture or rep can run the calcs for the flue. It would be hard for the owner or the chimney contractor to argue with that."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Thanks for reaffirming my calculations. Unfortunately we can't get a second opinion because the owner contracted the company separately. But since we are on this project with these guys, how can we approach this sizing issue without upsetting them even further? We can't just leave the sizing as such because at the end we will be responsible for proper boiler operation and we will be signing chimney portion of schedule C.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
Send them and the owner a letter documenting your calculations and recommendations based on the tables you used, either the manufacturers or NFPA 54?. If you proceed with their system and problems arise you have it in writing. Have them sign the letter.Bob "hot rod" Rohr
Living the hydronic dream1 -
Hot rod I would just flat out refuse if I knew for a fact it was wrong...no idea what schedule c is...hot rod said:Send them and the owner a letter documenting your calculations and recommendations based on the tables you used, either the manufacturers or NFPA 54?. If you proceed with their system and problems arise you have it in writing. Have them sign the letter.
fire the contractor and hire another one, that will give you time to sort out the required flue size, is the 275 boiler flue 8""The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
It sounds like the liner is already installed and the contractor doesn't want to change it.newagedawn said:fire the contractor and hire another one, that will give you time to sort out the required flue size, is the 275 boiler flue 8"
Bit late to just fire them, I think that's issue.
I also think @gennady is right, this is going to cause endless problems and they're going to be his problems.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I would write a letter voicing your concerns. Have the G.C. and the owner of the chimney company sign it, and maybe get it notarized.
Do you have a copy of the the proposal? It should state "X" boiler installed, connected to new "Y" chimney. All work to code, and per manufacturers specifications, yada, yada.
Bottom line is C.Y.A.!0 -
Ill say it again. Get the boiler manufacture involved. They have engineers on staff that do nothing but calc this stuff. Show the manufacture engineers calcs to the owner and tell them that the warranty will be void if the job is not done per manufacture spec.
I am sure you are right. You just need to send it to a higher authority to convince everyone else."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I agree that the chimney liner should be sized properly.
However, I must admit that I've been in countless basements and boiler rooms that had boilers vented into over-sized masonry chimneys. That being said, on a few occasions did we witness poor draft, unstable flame or unsafe conditions. An over-sized metal liner is probably better than no liner at all. If the new liner is 14 inch, I suspect the chimney interior is at least a 16" square and perhaps much larger.
If all three appliances are typical gas fired atmospheric equipment you may be just fine with the 14" liner. Keep in mind when just one of the water heaters is operating even the correctly sized liner (eight inch I gather) will be grossly over-sized!0 -
Absolutely.ScottSecor said:I agree that the chimney liner should be sized properly.
And with a 14" it's three times as bad as a correct setup. That's not the way to do things. a 14" pipe can in theory vent 3 times as much as an 8 inch.
I do get where you're coming from though. You're saying it's probably not the end of the world.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
As Bob stated , make sure the building owner or representative is also aware . A Hold Harmless Agreement is a powerful tool along with making others who disagree do a bit more critical thinking .hot rod said:Send them and the owner a letter documenting your calculations and recommendations based on the tables you used, either the manufacturers or NFPA 54?. If you proceed with their system and problems arise you have it in writing. Have them sign the letter.
You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38331 -
Can an oversized liner be compensated for with a specially selected chimney cap?Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Hi, The water heaters are unlikely to be able to heat up such a large vent... so spillage is almost a certainty. I'd get all parties involved and not allow this unsafe condition to be created.
Yours, Larry0 -
I have no idea why anyone would take responsibility for such a thing...They hopefully will tell the ocupents of the property the potential problem....Some one is making a real stupid decession, if I read the op correctly0
"Thanks everyone for the advice, I really appreciate it. As you mentioned, we will provide them with our calculations for their review and request theirs to prove that their sizing is correct. As of now we haven't been able to get any calculations from them. "Gennady Tsakh