Too hot hot water from oil burner

Bigdaddrock
Bigdaddrock Member Posts: 11
We have solar panels that heat water which gets kept in a holding tank, which then feeds into our oil furnace. In the summer, the water from the panels can reach as high as 150 degrees. As this feeds into the furnace, the hot water coming to our showers can sometimes be scalding to say the least.
Is there a way to install a "regulator" of some sort on the domestic hot water feed (for all except the baseboard heaters) to ensure that the temp never exceeds a particular temperature?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,600
    Thermostatic mixing valve. You should have one anyway, particularly for solar which can get lethally hot. Watts and Honeywell are good; there are a number of others.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Canucker
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,298
    edited June 2017
    What @Jamie Hall said is good advise.
    Canucker
  • HVACNUT
    HVACNUT Member Posts: 6,242
    edited June 2017
    What do you mean by the water from the holding tank feeds into the "boiler"? Do you mean its piped to a tankless coil on the boiler?
    If that's the case then what @Jamie Hall said is correct. You would install the mixing valve on the hot out of the coil. Good idea to install a well thermometer also so you can temper the valve to your needs. "Typical" domestic hot is 120 degrees.
    Also, what is the operating control on the boiler? Is it cold start, or does the boiler maintain a minimum temp.?
  • Steamhead
    Steamhead Member Posts: 17,333
    HVACNUT said:

    What do you mean by the water from the holding tank feeds into the "boiler"? Do you mean its piped to a tankless coil on the boiler?

    If that's the case then what @Jamie Hall said is correct. You would install the mixing valve on the hot out of the coil. Good idea to install a well thermometer also so you can temper the valve to your needs. "Typical" domestic hot is 120 degrees.

    Also, what is the operating control on the boiler? Is it cold start, or does the boiler maintain a minimum temp.?

    This.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • HVACNUT
    HVACNUT Member Posts: 6,242
    What?
  • Big Ed_4
    Big Ed_4 Member Posts: 2,989
    Hot water piped in series produces hotter water ,hot water in parallel produces more volume in hot water...