Galvanizes Piping
StephenPelosa
Member Posts: 20
I'm in Beijing China on a vacation and noticed in a museum that they used galvanized piping for a hydronic heating system. The system looks fairly new. I was wondering is this a good practice since I've never seen galvanized pipe for hot water heat. I'm just curious.
0
Comments
-
Is it threaded? I have seen stainless used also, either press, compression, or welded connections.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Galvanized pipe for hydronic heating is O.K. But black steel pipe is fine assuming that oxygen is eliminated from the circulating water. Black pipe is less expensive, so it is preferred.
For potable water, galvanized pipe is preferred over black.0 -
Hot enough water dissolves zinc oxide I think.0
-
galvanized pipe for domestic is not allow in US, but it can be for heating"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
I thought galvanized was still code compliant for domestic water?newagedawn said:galvanized pipe for domestic is not allow in US, but it can be for heating
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
But no glycols allowed in galvanized pipes or fittings.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
Hello, I don't remember the source, but I understand that galvanized pipe is being outlawed because sometimes lead is used along with the zinc to make it flow better when galvanizing pipe.
Yours, Larry0 -
As for my country , as far as I know , I have just seen that galvanized pipes with diameters of 2 " inches up to 6 " inches are being used for supply water and domestic hot water in skyscrapers and some commercial high rise complex buildings . However, i have not seen this type of pipe used for hydronic heating systems . But, I saw once that an older timer heating installer had used this type of the pipe for making welded collectors in a boiler room .
As for me , I hardly use it just for swimming pool and spa piping ,and making collectors for supply water and domestic hot water in boiler rooms .
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements