Viessmann comparison
Alan (California Radiant) Forbes
Member Posts: 4,212
I have a job coming up that has 1,200 square feet of radiant and a small DHW load. I have two Viessmann choices:
- Vitodens 222-F B2TB35 combi
or
- Vitodens 200-W B2HB-26 with a Combi PLUS DHW heat exchanger
Any preferences?
- Vitodens 222-F B2TB35 combi
or
- Vitodens 200-W B2HB-26 with a Combi PLUS DHW heat exchanger
Any preferences?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
To the best of my knowledge, the combi plus is only compatible with the existing
100 series. The combi plus add on is being phased out in favor of an all in one case design.To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
-
Thanks, guys. I suppose with the 25 gallon tank, the 222-F would reduce short cycling.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I've done a few 222-F boilers now. They have become my go to whenever possible. Indeed they do not short cycle. On small heating systems I use a Low Loss Header for the obvious benefit.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements