Wiring a Viessman Vitotronic 200 in conjunction with an existing 12 zone Taco system

TheJarman
Member Posts: 2
Greetings
I have just replaced a conventional oil fired boiler (that was controlled by an aquastat) with a new Viessmann Vitorond 100 and a Vitotronic 200 Control Unit.
Question is the aquastat on the old unit had T T inputs that were activated by the Taco relay firing the boiler on a demand for heat.
No such connection on the Vito 200 or the Pump Power Module.
The existing house has 9 Zones of radiant with mechanical mixing valves and 3 zones of hi cap baseboard with no mixing valves.
I do not want to redo the existing manifold and all of the circs along with the Taco relays....
How do I make everybody shake hands and play nice?
Also there is a boiler bypass with a circulator to inject supply water into the return header to keep the boiler from condensing. How do I control this circulator?
Thanks
I have just replaced a conventional oil fired boiler (that was controlled by an aquastat) with a new Viessmann Vitorond 100 and a Vitotronic 200 Control Unit.
Question is the aquastat on the old unit had T T inputs that were activated by the Taco relay firing the boiler on a demand for heat.
No such connection on the Vito 200 or the Pump Power Module.
The existing house has 9 Zones of radiant with mechanical mixing valves and 3 zones of hi cap baseboard with no mixing valves.
I do not want to redo the existing manifold and all of the circs along with the Taco relays....
How do I make everybody shake hands and play nice?
Also there is a boiler bypass with a circulator to inject supply water into the return header to keep the boiler from condensing. How do I control this circulator?
Thanks
0
Comments
-
The 200 will operate off of its reset curve. No TT connection is necessary; it's a smart control.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
so no connection of any kind between the boiler controls and the taco relays?
Thank you for the input.0 -
No need , the outdoor reset control will shut off the boiler when the outdoor temp rises to the set point ...I have enough experience to know , that I dont know it all0
-
Primary secondary piping .. There should be an connection in the control for the boiler circulator .. Size the circulator for was is recommended .I have enough experience to know , that I dont know it all0
Categories
- All Categories
- 84.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 421 Carbon Monoxide Awareness
- 58 Chimneys & Flues
- 1.8K Domestic Hot Water
- 5K Gas Heating
- 124 Geothermal
- 158 Indoor-Air Quality
- 3.2K Oil Heating
- 57 Pipe Deterioration
- 830 Plumbing
- 5.6K Radiant Heating
- 373 Solar
- 14.3K Strictly Steam
- 3.1K Thermostats and Controls
- 55 Water Quality
- 42 Industry Classes
- 83 Job Opportunities
- 24 Recall Announcements