Wiring a Viessman Vitotronic 200 in conjunction with an existing 12 zone Taco system

TheJarman
Member Posts: 2
Greetings
I have just replaced a conventional oil fired boiler (that was controlled by an aquastat) with a new Viessmann Vitorond 100 and a Vitotronic 200 Control Unit.
Question is the aquastat on the old unit had T T inputs that were activated by the Taco relay firing the boiler on a demand for heat.
No such connection on the Vito 200 or the Pump Power Module.
The existing house has 9 Zones of radiant with mechanical mixing valves and 3 zones of hi cap baseboard with no mixing valves.
I do not want to redo the existing manifold and all of the circs along with the Taco relays....
How do I make everybody shake hands and play nice?
Also there is a boiler bypass with a circulator to inject supply water into the return header to keep the boiler from condensing. How do I control this circulator?
Thanks
I have just replaced a conventional oil fired boiler (that was controlled by an aquastat) with a new Viessmann Vitorond 100 and a Vitotronic 200 Control Unit.
Question is the aquastat on the old unit had T T inputs that were activated by the Taco relay firing the boiler on a demand for heat.
No such connection on the Vito 200 or the Pump Power Module.
The existing house has 9 Zones of radiant with mechanical mixing valves and 3 zones of hi cap baseboard with no mixing valves.
I do not want to redo the existing manifold and all of the circs along with the Taco relays....
How do I make everybody shake hands and play nice?
Also there is a boiler bypass with a circulator to inject supply water into the return header to keep the boiler from condensing. How do I control this circulator?
Thanks
0
Comments
-
The 200 will operate off of its reset curve. No TT connection is necessary; it's a smart control.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
so no connection of any kind between the boiler controls and the taco relays?
Thank you for the input.0 -
No need , the outdoor reset control will shut off the boiler when the outdoor temp rises to the set point ...
There was an error rendering this rich post.
0 -
Primary secondary piping .. There should be an connection in the control for the boiler circulator .. Size the circulator for was is recommended .
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements