Burnham Boiler Piping
Thank you.
-Joey
Comments
-
The installer can say anything that he wants: it doesn't make it true.
The manual is the authority for the MINIMUM piping requirements, not an installer's opinion.
A few quick observations:
1. Sweated copper pipe should not have been used above the water line, especially on the risers out of the boiler or on the header.
2. The risers should not be Tee'd together but should enter the header separately.
3. There should be no horizontal piping until at least 24" above the boiler's water line.
4. The header is piped wrong and will result in wet steam being delivered to the system.
5. It looks like the installer didn't have a pipe threader so he short cut by using copper which could cause the block to crack.
Here's what a properly piped steam boiler looks like:
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Completely wrong but not the cause of a rotted section above water line, if in fact that is the immediate problemTo learn more about this professional, click here to visit their ad in Find A Contractor.1
-
Ask him to explain to you why he thinks that the boiler is piped correctly....
1 Ask him why he chose copper
2 Ask him why risers don't need 24 inches
3 Ask him to briefly explain to you how a steam system operates
4 Ask him why he deviated from the min. specs the manufacture
recommended.
5 Ask him for your money back,them show him the door...0 -
Where are you located? We may be able to recommend a competent steam contractor in your area.
For reference I would not allow the person who installed that to ever come into my house again.
Honestly it's so wrong I am not even sure where to begin describing the problems.0 -
The original installer had no business working on steam.
That said, I'd assume your rotted section is due to either leaks in the system (vents, radiator valves etc) and or your water quality.
That said, forget the original installer, unless he's able to get the block covered under warranty which is highly doubtful.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I am a novice at steam. Could the pin hole due too much fresh water being introduce into the boiler?0
-
Sorry for the back to back posts....but don't give up on chasing him for money back....You deserve something0
-
j a said:
Where is the pin hole....was a complete hydrostatic test done?mercedes said:I am a novice at steam. Could the pin hole due too much fresh water being introduce into the boiler?
He's not the op nor did he say he had a rotted boiler?j a said:Sorry for the back to back posts....but don't give up on chasing him for money back....You deserve something
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Now I am confused....or someone is confused..... I don't need a moderator....0
-
Judging from the stickers he is in New Hampshire.
That boiler is a total mess...
Manual never got opened.0 -
Why as one suggested thinking that Burnham will back him with a new block..I stand with Burnham on this one...if fact forbid him from purchasing any more boilers...he's giving the company a bad rap0
-
I'm in Northeast Massachusetts. I'm the homeowner. The boiler was replaced in the fall of 2008 with a change from oil to gas. I think they added the copper piping and fit it to the other existing pipes instead of replacing them all. I don't know exactly where the leak is, but steam was blowing into my chimney. Installer tried to get Burnham to cover the block under warranty, but the claim was rejected.0
-
@Charlie from wmass Is who you want.jmbreton said:I'm in Northeast Massachusetts. I'm the homeowner. The boiler was replaced in the fall of 2008 with a change from oil to gas. I think they added the copper piping and fit it to the other existing pipes instead of replacing them all. I don't know exactly where the leak is, but steam was blowing into my chimney. Installer tried to get Burnham to cover the block under warranty, but the claim was rejected.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
@jmbreton What is it you wish to gain or move forward with at this point? As stated the installation would void the warranty. It would also shorten the life of the boiler and increase your fuel consumption and reduce your comfort. The installer is lucky to not be charged with destruction of property and slander attaching his name to the Burnham boiler, and I am not a fan of their boiler but it lasts longer than 8 years if installed properly.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
I'm not sure where to go from here. I wanted the installer to fix it properly and not charge me extra for the work. All of this information today has been very helpful so I can ask them the right questions. I don't want a new boiler right now.0
-
Talk about crow flying the piping!!!!!!!! The shortest distance between two points...............................is a straight line.
and the installer said the piping was fine! He obviously never learned to read.0 -
You may not want a new boiler but, at this [point, that's the only way you are going to be reaady for next winter. If steam was blowing up your chimney, at least one of the sections is rotted out above the water line and, if one section blew, other sections are likely not too far behind. Bite the bullet and get that boiler replaced by someone who knows what he is doing. @Charlie from wmass is definitely your man. Do it now, not in the middle of nest winter when everybody will be extremely busy, your options will be far fewer and you'll end up with another botched installation.jmbreton said:I'm not sure where to go from here. I wanted the installer to fix it properly and not charge me extra for the work. All of this information today has been very helpful so I can ask them the right questions. I don't want a new boiler right now.
3
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements