We were called to look at a 1941-vintage hot-water system with recessed cast-iron convectors. The complaint was that two of the convector elements had cracked. Here's one of them- looked like a freeze-up but the customer swore it hadn't frozen:



We went down to the boiler room. The boiler is a mid-1950s American-Standard gas-fired unit, still running on gravity. It had a plain steel expansion tank, but the ends were dished outward instead of inward as we usually see.

The customer said this happened a short time after the fill valve was replaced. I asked to see the new valve. He removed the hatch in the ceiling and here's what I saw:



The "tech" who replaced the old dual control substituted a backflow preventer for the safety valve. There was no safety valve on the boiler itself- this setup was OK back then but doesn't meet Code now. I'll bet the expansion tank had lost its air cushion, and that's what caused the excessive pressure.

This system is in a rowhouse. Think what would have happened if it had exploded.

YOU CAN'T FIX STUPID!!!

I know one of the owners of the company whose employee did this, and have a call in to him. I'll update this with more pics as we go.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
JohnNYSolid_Fuel_Man

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,061
    Options
    I came across the similar situation. Combo fill/PRV was dripping. Tech replaced combo with new, he got a call from HO that his new part was dripping....he returned and "fixed" that problem with a plug for the PRV discharge. Then he returned to bleed air out of 2nd floor rads. That lost the only air storage there was. One rad started dripping between sections.
    Changed out the boiler for other reasons, it now has 2 PRV's.
    The dripping rad cured itself with pressure lowered.

    This could have turned into the same disaster you prevented.
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,239
    Options
    Nice catch! You may have saved a lot of life's. So pat yourself on the back.