hartford loop?
newagedawn
Member Posts: 586
i have a question about the return side of the hartford loop, can the boiler side return and the hartford loop side return where the main returns come down, be at the same level or should there be an offset to the two wet pipes
"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"
0
Comments
-
Doesn't matter. The main thing is that the top of the Hartford loop should be below -- but not much below -- the low water line of the boiler, and it has to be connected at the top to the equalizer. Beyond that -- pretty much anything goes.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England-1 -