header to mains?
newagedawn
Member Posts: 586
in Oil Heating
hello, i have a 1 piper, 2 mains at 2 1/2" , can i run 2" to connect to the existing 2 1/2" pipe from the header or should i keep it 2 1/2 from header
"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"
0
Comments
-
Should keep it 2 1/2"Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Yes as @Jamie Hall said it really should be 2 1/2". I know you won't like that answer.
If you decide to cheat make sure too use eccentric reducers flat on the bottom. And only if you
I wouldn't do it without checking the connected EDR against the pipe size. You may find some radiation has been removed and you can squeak by with 2"
If you have someone good that can measure you may be able to make it up with nipples or find someone with a 2 1/2" pipe machine.
Some supply houses can cut and thread or (here comes the incoming fire) find a welder
what size is your header??0 -
Just use pre-cut nipples, as we do.
What boiler are you installing?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting-1 -
peerless ec-03 with a 3 inch header and 2 inch equalizer, just wondering if i can run the mains from the header 2" to connect to the 2 1/2 mains that exist"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
-
What is the connected radiation of each main?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements