Condensing Noritz CB199 ng Pluming Issue
Bigtrucker821
Member Posts: 8
I recently had a cb199 installed with radiant baseboard fin I am totally unhappy with the performance had the installer back a couple of times he made some adjustments still not happy. In NY the weather is unpredictable last week 20d 80 mile hr winds could not get the house to 70d. Saw a post from Gordy about a similar unit from looking at the post pictures I believe my pluming to the secondary loop and primary loops are incorrect. I have tried to contact Noritz to get a pluming diagram with no luck. I need supportive information to address my concerns with the installer any help would be appreciated
0
Comments
-
http://www.noritz.com/products/cb199-2/
Install manual is on the website about halfway down that page.0 -
See webpage: http://www.noritz.com/products/cb199-2/
Click link for manual.
Typ zone valve piping pg 36
Typ zone pump piping pg 37Terry O0 -
Have that information but need a more detailed diagram for the loop coming from the combo unit and the hookup to the primary heating loop thanks0
-
That's as detailed as you're going to get as far as installation piping applications. Why don't you post some photos of your installation so we can see what your guy did.Bigtrucker821 said:Have that information but need a more detailed diagram for the loop coming from the combo unit and the hookup to the primary heating loop thanks
ETA: also post some details like what your heat loss is and how many feet of finned baseboard you have0 -
This is my problem area on the bottom of unit0 -
If those two Tees in the orange pex on the left side are for spaceheating loop... per the manual they're way too far apart:
"All closely spaced tees shall be within 4 pipe diameters center to center spacing"
It looks like they're 7-8" from center to center?
If the orange pipe is 1" pex... they should be 4" apart center to center.
Can you even use pex for the boiler loop? 1" pex carries considerably less water than 1" copper... especially when you throw a few restrictive pex elbows in the mix.0 -
The observation you made is the same conclusion i came to except the loop to the left is the primary heating loop and the installation manual requires the boiler secondary to be installed INTO the heating loop at the 4" spacing these appear to be installed incorrect orientation whats your take on this. IM not comfortable with the PEX either old school0
-
Sorry I don't have any experience with P/S piping, but it looks like it would be a 20min job to make your current layout conform to the layout recommended in the install manual.
You could reuse the two Tee's and elbows, you'd just need a couple of feet of 1" OB pex, some 1" pex clamps and the crimp tool.0 -
Wow... Is there another circulator pump besides the one in the "boiler"0
-
Yes next to the zone valves on return run loop out of picture0
-
Yes to above comments as to the "proper implementation" of primary secondary piping. Those pex fittings are very restrictive. Tell us about the heating emitters other than fin tube. How long are the loops? How many feet of fintube on each loop? And the pump on the heating loop size?0
-
Thanks Gordy the installer is telling me that he has done bigger houses with the same installation procedure as my unit and no problems no complaints he doesn't agree with the manual i am working on setting up a meet with a support tech and the installer to check out the installation and what might be the problem very unhappy with the performance of this unit do you think if the loops are tied in incorrectly it would effect the performance of the comboi unit0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements