Radiator stays hot when closed.
kurdt
Member Posts: 3
So I just moved into an apartment building that uses old cast iron radiators. there is only one valve on the left of the radiator that says 'open' with an arrow going counter clockwise. It had got really cold, naturally being in Canada, so I opened the valve to fill up with hot water. I closed the valve after 30 sec and it is still very hot after weeks of initially opening it. Now, the radiator in my bedroom, is boiling hot on the right side and warm on the left where the valve is, of which I have never opened. How do I turn the heat off, I can't sleep because it's a thousand degrees!
0
Comments
-
Is this a steam system, not hot water? Is that correct? Is there a vent mounted on the left side of the radiator, opposite the valve? If so, it is a one pipe steam system. Turn that vent upside down. That will prevent air from escaping and steam from getting into the radiator. Many, if not most of those old radiator valves don't shut off anymore. After you turn the vent upside down, open the valve all the way open again and leave it that way. That will allow any condensate in the radiator to drain back to the boiler.0
-
> @Fred said:
> Is this a steam system, not hot water? Is that correct? Is there a vent mounted on the left side of the radiator, opposite the valve? If so, it is a one pipe steam system. Turn that vent upside down. That will prevent air from escaping and steam from getting into the radiator. Many, if not most of those old radiator valves don't shut off anymore. After you turn the vent upside down, open the valve all the way open again and leave it that way. That will allow any condensate in the radiator to drain back to the boiler.
I don't see anything on it that I can turn upside down. Here are some pictures, although the only thing I can play with is the 'open' valve.0 -
That's a Vapor system. Sounds like the shutoff valve isn't holding. I'd be willing to bet the steam pressure in this system is running way too high, and that's keeping the valve from closing tightly.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
To which I will add -- if the pressure is too high, as is very likely, it doesn't take much of a leak across the valve to allow the radiator to heat just splendidly.Steamhead said:That's a Vapor system. Sounds like the shutoff valve isn't holding. I'd be willing to bet the steam pressure in this system is running way too high, and that's keeping the valve from closing tightly.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
So the answer is, contact the management, and ask them about the maintenance of the system. They are wasting a lot of fuel by not paying attention to the pressure. Direct them here for answers to any questions they may have.--NBC0
-
If the side of the rad without the valve is getting hot, then you may have steam coming up your return line thru the trap device into the radiator.
There should be no steam in the return line, the small pipe. Steam is kept out of the return pipes by traps of which some could be failed and allowing your rad to over heat even with the valve closed.
Also many unknowingly turn the pressure on the boiler too high which may keep some tenants happy and overheat others.
This situation is costing the landlord a lot of money, he needs a pro to check the system out.....you have to spend a little to save a lot.0 -
In the meantime, throw a blanket on the radiator, or a part of it, or get some cardboard or Styrofoam and fashion out a cover.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements