Is a Honeywell 3-wire R182A 1004 relay a suitable replacement for an R19A1K 3-wire relay?

Skibum05
Member Posts: 2
This is for powering on my circulator pump. The Honeywell R19A1K -- 3's relay has quit working, and I cannot find JUST a replacement relay to solder into the old relay box, so I'm looking to replace the entire relay box. Unfortunately I can't find any R19A relay boxes for sale anywhere (eBay, Craigslist, Amazon, HVAC dealers, etc.) to use with my bi-metal Series 10 3-wire thermostat. The Honeywell 3-wire R182A 1004 SPST relay sure looks and sounds like it will work. Would just like to confirm before I spend unnecessary money on eBay.
Thanks to anyone who knows!
Ski - Cincinnati
Thanks to anyone who knows!
Ski - Cincinnati
0
Comments
-
Yes the R182 can be used. Both are Series 10 DPST thermostat controls wired R=W=B. You could also go with a two wire thermostat and use an R845 relay. You would drop the R red wire.0
-
Perfect! Thanks so much for confirming what I thought to be true. Yes, also realize I could "upgrade" to a 2-wire t-stat as an alternative.
Ski0
Categories
- All Categories
- 84.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 421 Carbon Monoxide Awareness
- 58 Chimneys & Flues
- 1.8K Domestic Hot Water
- 5K Gas Heating
- 124 Geothermal
- 158 Indoor-Air Quality
- 3.2K Oil Heating
- 57 Pipe Deterioration
- 830 Plumbing
- 5.6K Radiant Heating
- 373 Solar
- 14.3K Strictly Steam
- 3.1K Thermostats and Controls
- 55 Water Quality
- 42 Industry Classes
- 83 Job Opportunities
- 24 Recall Announcements