Proper Tankless Coil Setup
Hilly
Member Posts: 428
1. Are Multi-Orifice Flow Control Valves (ie. Watts P3) required?
2. Should they be piped with 2 Shut-offs, 2 Tee's and 2 Dran-taps for future flushing?
I ask this question because I got a picture e-mailed to me stating they need the domestic copper on 'their furnance' replaced because they both leaked on the oil company doesn't service domestic side of boiler under service contract. They say there is pex at the ceiling and they'd like to tie back to that point.
So code around here - Canada, although nobody looks at heating in my province - says 3' of copper of the boiler. So I was going to put in the 2 Shut-offs, 2 Tee's and 2 Dran-taps and bring copper up to horizontal transition.
Question comes down to, do I put the P3 back in. Do I move it to the cold line, if so, where the manufacturer says it belongs. If I can omit it, there where exactly are these meant to be use, it is on really old coils that maybe had a different make-up and the flow needed to be controlled to keep up with the heat transfer? I just know if I leave it out, I will be asked why and I like to have answers. Also I e-mail NYI and they responded leave it out but with no explanation.
2. Should they be piped with 2 Shut-offs, 2 Tee's and 2 Dran-taps for future flushing?
I ask this question because I got a picture e-mailed to me stating they need the domestic copper on 'their furnance' replaced because they both leaked on the oil company doesn't service domestic side of boiler under service contract. They say there is pex at the ceiling and they'd like to tie back to that point.
So code around here - Canada, although nobody looks at heating in my province - says 3' of copper of the boiler. So I was going to put in the 2 Shut-offs, 2 Tee's and 2 Dran-taps and bring copper up to horizontal transition.
Question comes down to, do I put the P3 back in. Do I move it to the cold line, if so, where the manufacturer says it belongs. If I can omit it, there where exactly are these meant to be use, it is on really old coils that maybe had a different make-up and the flow needed to be controlled to keep up with the heat transfer? I just know if I leave it out, I will be asked why and I like to have answers. Also I e-mail NYI and they responded leave it out but with no explanation.
0
Comments
-
Flow control is used so that you don't overdraw the coil. As far as I know it is not code required. (could be in your area??)
for instance most tankless coils are rated at 200 deg. F boiler water temp. Most of the time the boiler water isn't that hot.
so if we had a tankless rated at say 5gpm with 200 deg boiler water we would sometimes put a 3 gpm flow restrictor on it to make sure they didn't run out of HW.
0 -
The question really is -- what is the temperature rise capability of the tankless coil at various flow rates? The purpose of the P3 is to limit the flow through the coil to something which will produce hot enough water. So you really need to know what the tankless coil can do.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements