Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Slant/fin model em-10 electric boiler control. Alarm goes off

I have one and when it starts to go up to stage 4 an alarm goes off and shuts down. I'm sure it's either an electrical issue or bad relay. Where would I start.

Comments

  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261
    Check 2 things for starters. Check your incoming voltage while in stage 4. Check your flow through the boiler. Do you have a flow switch installed? what does the outlet temp go to when stage 4 kicks in?
    ralph1956
  • Keith M
    Keith M Member Posts: 78
    The EM-10 is an OEM control we source from Tekmar. I have a call into our Tekmar representative on this. Normally the alarm will go off if there is a sensor issue. However, I think you may be hearing noise coming from a reply. I suggest you contact Slant/Fin Technical Services about this. Below is the USA and Canadian phone numbers, please call the appropriate number for your location.
    USA - 516 484 2610
    Canada - 905 677 8400
    Thank you,
    Keith Muhlmeister
    Slant/Fin Corporation
    Harvey Ramerratioralph1956
  • ratio
    ratio Member Posts: 3,789
    You're slipping, Keith...that came through yesterday... :wink:
  • Keith M
    Keith M Member Posts: 78
    Yup, what can I say?