When you say "lifted the steam inlet" Did you pitch the rad towards that inlet/valve? That valve/"inlet" should be on the low end of the rad. Just wanted to be clear.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
Sounds like 2 pipe steam here, so inlet/valve to radiator should be at high end, outlet/trap at low end.Grallert said:When you say "lifted the steam inlet" Did you pitch the rad towards that inlet/valve? That valve/"inlet" should be on the low end of the rad. Just wanted to be clear.
0 -
Yes of course my mistake. Careless reading.Abracadabra said:
Sounds like 2 pipe steam here, so inlet/valve to radiator should be at high end, outlet/trap at low end.Grallert said:When you say "lifted the steam inlet" Did you pitch the rad towards that inlet/valve? That valve/"inlet" should be on the low end of the rad. Just wanted to be clear.
The hammering could be coming from somewhere other than but maybe near that rad. I would guess that there is water spending too much time in one of the supply pipes associated with that area or that rad. Have you checked pitch of the piping?Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
All of the piping is hidden in the walls. It is a two pipe system with the steam entering the radiators at the top on one side and exiting the bottom of opposite side through a radiator steam trap.
0 -
-
Do you actually hear the hammer in the radiator or does it sound like it might be in the supply pipe? If it's actually in the radiator, I'm wondering if the return side of the radiator might have a build up of crud in it causing a build up of condensate before it is able to drain through the trap. Did you look in that end of the radiator when you replaced the trap or did you just replace the element in the existing trap?0
-
This radiator is fed by a vertical riser.Jamie Hall said:Somewhere on the feed to that radiator there is a low spot -- bad pitch or a sag. It takes very little. Until you find it...
0 -
The hammer is actually hitting the shut off valve to the radiator and the radiator is fed from a vertical riser.Fred said:Do you actually hear the hammer in the radiator or does it sound like it might be in the supply pipe? If it's actually in the radiator, I'm wondering if the return side of the radiator might have a build up of crud in it causing a build up of condensate before it is able to drain through the trap. Did you look in that end of the radiator when you replaced the trap or did you just replace the element in the existing trap?
0 -
Well then, figure out what is suspending a slug of water in that vertical pipe in such a way that it can hit the shutoff valve. I can't think of one, but...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Are you 100% sure the radiator is fed from a vertical straight up into that valve? Is this radiator on the first floor? It would still have a horizontal run-out from the main. If it is on the second floor, unless it is recessed in a wall, or the steam pipe is outside the wall, in the room below, it has to have a small horizontal section under the floor.dave_myrick66 said:
The hammer is actually hitting the shut off valve to the radiator and the radiator is fed from a vertical riser.Fred said:Do you actually hear the hammer in the radiator or does it sound like it might be in the supply pipe? If it's actually in the radiator, I'm wondering if the return side of the radiator might have a build up of crud in it causing a build up of condensate before it is able to drain through the trap. Did you look in that end of the radiator when you replaced the trap or did you just replace the element in the existing trap?
Is their any nipple between the radiator and the supply valve that may be bushed down significantly and holding water0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements