Identical Pumps in Series vs. Parallel - flow rates vs. power consumption vs. longevity
tivo
Member Posts: 16
Two identical pumps piped in series vs. parallel:
Q1: Will either piping yield double the system flow rates?
Q2: Will the power consumption be equal in both cases?
Q3: Will either piping affect the life expectancy of the pumps? Just thinking the pumps piped in parallel might be working "harder" overcoming higher head vs. pumps in series sharing the resistance. But then, when the head/resistance is shared, the pumps in series work at a higher flow rates, i.e. potentially more wear and tear so to speak... so I can't draw a conclusion... as you can already tell, I'm no engineer.
Thanks in advance.
Q1: Will either piping yield double the system flow rates?
Q2: Will the power consumption be equal in both cases?
Q3: Will either piping affect the life expectancy of the pumps? Just thinking the pumps piped in parallel might be working "harder" overcoming higher head vs. pumps in series sharing the resistance. But then, when the head/resistance is shared, the pumps in series work at a higher flow rates, i.e. potentially more wear and tear so to speak... so I can't draw a conclusion... as you can already tell, I'm no engineer.
Thanks in advance.
0
Comments
-
Q1. No. Parallel will almost double, but not quite -- how much off will depend on the system and pump head vs. flow curves. Series will also increase flow, but not double -- again, depending on the system and pump head vs. flow curves.
Q2. In general, no. Depends on the efficiency characteristics of the pumps. However, it may be less power -- or it might be more.
Q3. In most cases, no. In the rare situation that the increased flow causes a sufficiently low NPSH at the pump intake, you might, just possibly, cavitate, which will reduce the life expectancy considerably. Depends on the intake conditions.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Hi Jamie, thanks for your quick response. Could you elaborate a little more on "depending on the system and pump head vs. flow curves"? I'm asking the questions assuming everything stays unchanged, same system, no other pumps other than these two within the system, and they are identical pumps hence identical pump curves. Let's assume boiler doesn't exist or simply assume this is a closed system with nothing but two pumps in it. I'm just trying to draw a simple conclusion, if there exists.0
-
One way to know would be to create a system curve then overlay it on the pump curve(s)
Some good pump basics, including how to develop a system curve in this journal.
http://www.caleffi.com/sites/default/files/coll_attach_file/idronics
\_16_na_0.pdf
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements