Ignition and run problem PUZZLING!!!
132mcg
Member Posts: 4
in Oil Heating
I'm having an issue with a Beckett oil burner, when my transformer is ajar, the furnace will ignite and run fine. If I push the transformer down to latch it, I lose my fire. If I undo the clips, the fire comes back. Any ideas?
0
Comments
-
Check the alignment between the transformer springs and the electrodes.
It's also possible that there's too much air to the burner or too little oil being atomized.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Thank you, I'll check it out.0
-
I've checked alignment of transformer to electrodes, it's all in check. Is it possible I'm not getting enough air for combustion due to a problem with the cage or coupler?0
-
No, not enough fuel or too much air.
When was the last time the nozzle and filter were changed?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Nozzle and filter are new, it calls for a .50x80A, I had a .60x80B and it ran great. Put new pump in as old one wouldn't hold pressure, tried putting in the 50 nozzle and it wouldn't light or run.0
-
-
It would have been easier to diagnose if you would have mentioned changing the pump from the beginning.132mcg said:Nozzle and filter are new, it calls for a .50x80A, I had a .60x80B and it ran great. Put new pump in as old one wouldn't hold pressure, tried putting in the 50 nozzle and it wouldn't light or run.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Set it up using Beckett's residential burner guide which will get you in the ballpark, then fine tune with combustion tester.0
-
What was the pump pressure on the old pump? It may have been running 140 PSI. The new ones are 100 out of the box. That will lower your firing rate, and all adjustments are set for a higher rate.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements