Use steam boiler water for indirect water heater?

Timco
Timco Member Posts: 3,040
I'm going to get that replacement I pictured below.

They want to upgrade from the original DHW tank and tiny Raypak.

Why can't I take steam boiler water with a pump below the water line and an aquastat for DHW off this 800k steamer? Anyone done this before?
Just a guy running some pipes.

Comments

  • EzzyT
    EzzyT Member Posts: 1,295
    edited January 2017
    Yes it can be done and it's done all the time.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Timco
    Timco Member Posts: 3,040
    So controls. Best way to wire this? Tekmar?
    Just a guy running some pipes.
  • Timco
    Timco Member Posts: 3,040
    I'm thinking I'll need a HX in line? Then I'll just need a storage tank and not an indirect?
    Just a guy running some pipes.
  • EzzyT
    EzzyT Member Posts: 1,295
    Are you going with atmospheric or wet based boiler? Tekmar control for outdoor reset?
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • EzzyT
    EzzyT Member Posts: 1,295
    What is your domestic hot water demand?
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Timco
    Timco Member Posts: 3,040
    EzzyT said:

    Are you going with atmospheric or wet based boiler? Tekmar control for outdoor reset?

    It's a Peerless atmospheric 800k steamer. Got pricing on 2 60 gal super store. Getting pricing on a plate HX and pumps now. I was thinking tekmar to control the boiler / DHW calls. I haven't set one up like this before.
    Just a guy running some pipes.
  • EzzyT
    EzzyT Member Posts: 1,295
    Personally I wouldn't go with a flat plate HX. You just need a standard switching relay no need for a tekmar
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • jumper
    jumper Member Posts: 2,245
    AERCO's original business was water heaters. A storage tank with flexible copper coils inside. Worked with steam or hot water. Steam powered ones were preferable. No pump for one thing. With 800k steam you don't need much storage for house.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,517
    What is your domestic hot water demand? It can't be larger than the boilers pick-up factor
  • Timco
    Timco Member Posts: 3,040
    > @EBEBRATT-Ed said:
    > What is your domestic hot water demand? It can't be larger than the boilers pick-up factor

    32 units, figure 2.5 per unit. The Raypak in there now condensed to death.
    Just a guy running some pipes.