Use steam boiler water for indirect water heater?
Timco
Member Posts: 3,040
I'm going to get that replacement I pictured below.
They want to upgrade from the original DHW tank and tiny Raypak.
Why can't I take steam boiler water with a pump below the water line and an aquastat for DHW off this 800k steamer? Anyone done this before?
They want to upgrade from the original DHW tank and tiny Raypak.
Why can't I take steam boiler water with a pump below the water line and an aquastat for DHW off this 800k steamer? Anyone done this before?
Just a guy running some pipes.
0
Comments
-
Yes it can be done and it's done all the time.0
-
So controls. Best way to wire this? Tekmar?Just a guy running some pipes.0
-
I'm thinking I'll need a HX in line? Then I'll just need a storage tank and not an indirect?Just a guy running some pipes.0
-
Are you going with atmospheric or wet based boiler? Tekmar control for outdoor reset?0
-
What is your domestic hot water demand?0
-
It's a Peerless atmospheric 800k steamer. Got pricing on 2 60 gal super store. Getting pricing on a plate HX and pumps now. I was thinking tekmar to control the boiler / DHW calls. I haven't set one up like this before.EzzyT said:Are you going with atmospheric or wet based boiler? Tekmar control for outdoor reset?
Just a guy running some pipes.0 -
Personally I wouldn't go with a flat plate HX. You just need a standard switching relay no need for a tekmar0
-
AERCO's original business was water heaters. A storage tank with flexible copper coils inside. Worked with steam or hot water. Steam powered ones were preferable. No pump for one thing. With 800k steam you don't need much storage for house.
0 -
What is your domestic hot water demand? It can't be larger than the boilers pick-up factor0
-
> @EBEBRATT-Ed said:
> What is your domestic hot water demand? It can't be larger than the boilers pick-up factor
32 units, figure 2.5 per unit. The Raypak in there now condensed to death.Just a guy running some pipes.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements