I have a 1100 square foot bungalow on slab with infloor radiant heating. 2 zones, hot water is obtained from a 65 Gallon Hot water tank that runs off natural gas. Heating bills are pretty good, the highest month for the past 5 years here in southern Ontario was $135. My plan is to replace the 1999 hot water tank and have considered maybe going with a tankless hot water tank. Upfront cost is much more but my main questions are:
Q1: Will a tankless hot water tank work with my infloor radiant system?
Q2: Will the tankless hot water tank cycle frequently?
Q1: Will a tankless hot water tank work with my infloor radiant system?
Q2: Will the tankless hot water tank cycle frequently?
0
Comments
-
Don't do it; you'll regret it!
Tankless water heaters are not designed, controlled or approved for space heating. The heat exchanger has an enormous amount head that will choke the flow produced by a hydronic circulator.
Most manufacturers will only warranty them for 3 years or less if used for space heating.
Use the right tool for the job: a boiler. It will be a lot more efficient than a tank water heater if done correctly.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.-1 -
I would NOT use a tankless to run your system. Do you also use the water heater to get your domestic hot water?
0 -
Yes there is just one hot water tank for both. I was not set on getting a tankless but wanted to explore if it was a good idea. I am willing to just replace the current hot water tank with a similar one no problems, way cheaper also. Just as a point the temp that my floor works at is 110 F.0
-
Sorry.. but whenever I hear "I want a tankless hot water heater" I always think of this:
https://www.youtube.com/watch?v=vffdymvjluk
The information may be presented in a silly way but the information is all true.2 -
I listened to it, great and true points. Good post.0
-
You should really separate the Heating from the domestic hot water.
A good Modulating boiler w an indirect water heater would be perfect. If space is an issue you could go the combi route. A bit of a trade off w the boiler being oversized but its better tha you have now.
I personally like this unit.
http://ibcboiler.com/ibc-products/hc-series/2
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements