One pipe residential, pressure gauge doesn't register
Comments
-
What does the gauge look like?0
-
-
-
Thank you for the quick replies - boiler is not short cycling, though sometimes having trouble getting large radiators hot all the way across (except on really cold days when the heat very well) - I'll confirm the range of the gauge to you later, I am certain it is a lower range, definitely not 0-60.0
-
That's exactly how the radiators should heat. Not all the way across when outside temps are moderate, more hot when outside temps are cold/closer to design day. Don't mess that up. Do add a 0-3 PSI gauge to your boiler. It will let you see what is actually happening, pressure wise.Fatbackbeat said:Thank you for the quick replies - boiler is not short cycling, though sometimes having trouble getting large radiators hot all the way across (except on really cold days when the heat very well) - I'll confirm the range of the gauge to you later, I am certain it is a lower range, definitely not 0-60.
-1 -
Radiators aren't expected to heat all the way across most of the time.
The more you heat a radiator, the more you heat the room. Heating them all the way across on a 40F day isn't going to be very comfortable or efficient.
Are your rooms all comfortable?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment-1 -
I was going to ask the same question - I just got a 0-3 psi gauge, and it registers two tiny marks above 0 after it's been running awhile.... Also, after several cycles, it shows a negative pressure (which re-sets when I unscrew the gauge temporarily). Normal?
Thx!0 -
Marcusjh, you must be operating in the ounce range. When the burner shuts off the steam begins to condense/ collapse creating a low vacuum in the system. After the air vents open and air enters the piping the gauge should return to zero.0
-
Yeeup.... the main vents are old Hoffmans and need to be updated.... so thar's the problem I guess. The operating pressure is ok though I'm assuming? I would have thought the needle would have gone higher, but she's barely moving. Once new main vents are put in, would that change?0
-
May I humbly suggest that if the gauge is reading in ounces when the system is running, and it drops into a slight vacuum when it stops... the Hoffmans are doing a completely adequate job. There is no need to change them.marcusjh said:Yeeup.... the main vents are old Hoffmans and need to be updated.... so thar's the problem I guess. The operating pressure is ok though I'm assuming? I would have thought the needle would have gone higher, but she's barely moving. Once new main vents are put in, would that change?
If it ain't broke, don't fix it.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'd add "..and the system is well balanced." to that.Jamie Hall said:
May I humbly suggest that if the gauge is reading in ounces when the system is running, and it drops into a slight vacuum when it stops... the Hoffmans are doing a completely adequate job. There is no need to change them.marcusjh said:Yeeup.... the main vents are old Hoffmans and need to be updated.... so thar's the problem I guess. The operating pressure is ok though I'm assuming? I would have thought the needle would have gone higher, but she's barely moving. Once new main vents are put in, would that change?
If it ain't broke, don't fix it.
A system can have a gorton D on 10-12 rads and never raise an ounce of pressure-1 -
Ok, great to know that the vacuum isn't a big deal, and the pressure is good. Thanks! BUT, takes 45 to 50 minutes for the radiators to start to get hot - so I'm still thinking the vents are too old & small (was told in another thread).0
-
Well, maybe. There are two stages to the process before the radiators start to get heat: getting the kettle up to a boil and getting the resulting steam to the radiators. Bigger vents or more of them will affect the second stage, but not the first.
What you need to do is to take the time from when the boiler starts to produce steam -- the header gets steam hot -- to when the radiators start to get steam. If that time is long -- anything much over two minutes for each ten feet of main is long -- then yes, more venting may help.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements