Mounting the Taco 007e with pics added
JimQ
Member Posts: 6
Hi Folks: I just had a new heating system installed which utilizes the new Taco 007e circulators. After it was installed I read the literature for all the equipment. According to the Data Information sheet on these valves, the electrical connections should be in the 9 o'clock position. For some reason, the installer put the two heating zone circulators in upside down with the connections in 3 o'clock position. The one that goes to the indirect water heater is mounted horizontally with the connector in the six oclock position. I think I will call the contractor and inquire, but I wanted to ask you folks for your opinions? Thank You.
0
Comments
-
Call the contractor, show him the instructions. Either he will fix them, or tell you that he always does it that way and never had a problem.
But he should fix them.
From Taco
"...Any Taco product or part not installed or operated
in conformity with Taco instructions or which has
been subject to misuse, misapplication... will
not be covered by this warranty"There was an error rendering this rich post.
0 -
The orientation of the electrical connections should not effect operation. The way the circ (shaft) is oriented is very important.
Do you have a picture?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I will get pics later today. Thank You for your rersponse! Jim0
-
usually the motor can be rotated in the volute by removing 2 or 4 allen bolts. It will involve isolating the pump from the system to do that.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I suspect the reasons are due to water possibilly hanging out in the box.
You're not alone, many contractors make this mistake.
Just FYI, some contractors have fragile egos. Like everything in life you have to pick your battles.. then again some homeowners treat contractors like second-rate citizens. The toils of living in a first-world society0 -
@JimQ
There are two things we look for as the most important when mounting any circulator;
1. That the motor is horizontal (for proper lubrication of the bearings and air removal)
2. that the electrical box is not below the motor (any water leaks and it doesnt short the system out) Electric above water.
So the instructions state the 9 o'clock position so that the print is in the proper orientation, the 3 o'clock position is just opposite depending upon the flow direction that was needed for your system. It can be taken apart as @Hotrod says just so the label is properly positioned.
Dave H.
Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -
I hope these images come through. I will call and request the body of the valves be rotated. The horizontal one to the water heater will have to have a longer wire installed when rotated. It makes sense for the electrical connection not to be below the water (Thanks Dave H)0
-
-
I'm a stickler, our installs always have the lettering in the regular orientation. Takes 2 minutes or less to rotate the motor.0
-
-
Bob: Is that a problem? I have no idea. I was told by the installer zone valves will work on either side if the boiler.0
-
-
Old habits die hard... some guys insist that the return is the correct place for circs. It will probably work just fine. As well as the 007e lettering being upside down, just unprofessional looking.
I'd rotate them, just for my OCD....but the one for the indirect should absolutly be rotated OCD or not.
The best place for circulators is on the boiler supply after the expansion tank. But on small residential jobs installers often get away with putting them on the return, rendering things less efficient, but still effective.
There is real science to back this all up, but you will probably be ok just rotating the circulator on the indirect.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Here is a good explanation and drawings of the pumping away concept.
http://smartgreenbuild.com/blog/download/591/
Gift the installers a copy of "Pumping Away" from the bookstore here.
If there are zone valves in the system you have 100% shutoff. if not you may experience un-wanted flow in zones when the thermostat is off, called ghost flow.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thank You all for your advise. I set up an appointment and the installer will make the necessary changes.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements