Pity the young new homeowners: Not one, but two boilers corroded above the water line in the rear section and steaming up the chimney.


New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com

Comments

  • New England SteamWorks
    New England SteamWorks Member Posts: 1,526
    There's only one solution for this mess: MegaSteam!



    The system was split in two, probably when these two boilers went in. We are going to put it back together.

    Heat goes down tomorrow. Busy day in store, down to 25º and snow, but it couldn't wait. We had to add water to one boiler every two hours, and it ran constantly...
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    IronmanGregWeiss
  • Fred
    Fred Member Posts: 8,542
    What a shame, and all that copper too!
    New England SteamWorksMilanD
  • LionA29
    LionA29 Member Posts: 255
    Sad!
  • Fred
    Fred Member Posts: 8,542
    Looking great!
    New England SteamWorks
  • EzzyT
    EzzyT Member Posts: 1,344
    Looks great
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    New England SteamWorks
  • upstateben
    upstateben Member Posts: 33
    I cant help but notice the water heaters are fed by gas. @RI_SteamWorks if i may ask, how did you sell the customer on oil when so many people are running away from it? Also the installation thus far looks fantastic as always.
  • Ironman
    Ironman Member Posts: 7,555
    Show some more pics when you're done.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,526
    edited January 2017
    As to those folks "running away", -there are none so blind as those who will no see. There is no better steam boiler, and no better protection against the dreaded chlorides than MegaSteam. It is oil only. And there is no better service than the service from your friendly neighborhood oil man. Every time you buy oil, or every time you buy gas, there is a profit in there. The difference is, a lot of the profit in the oil redounds to the customer. The profit from the gas is never to be seen again.

    If you are a gas customer we take very good care of you.

    But if you are an oil customer, you own me. Twentyfour seven. Threehundred sixty five. For life.

    I don't find it difficult at all to be honest.

    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    upstateben
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,526
    More: Steam boilers need annual service. They need their pigtails and low water cutoffs cleaned, the wet returns (and sometimes boiler) blowdown, sight gauge cleaned, someone to pay attention to the readings on the VXT, in addition to an overall inspection. If you are an oil customer, your get that every year. Guaranteed. If you're gas, -you never have it until it's too late and there's a problem. And then who do you call?
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    LionA29upstateben
  • upstateben
    upstateben Member Posts: 33
    My comment was made not as a plug for gas but just out of admiration of your ability to retain oil clients when gas is clearly in the home.
    New England SteamWorks
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,526
    > @Ironman said:
    > Show some more pics when you're done.

    Promise. Ilka's looking for another 15 minutes of fame, I'm sure!
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Fishin_Rod
    Fishin_Rod Member Posts: 31
    My boiler looked just like the ruined ones. A cast iron end section rotted out in just over one year. The installer replaced it under warranty, and said is was a casting defect. Four more sections went out over the next two years. Labor costs are killing me, and the manufacturer said no more - it must be a problem on my end.

    What is the correct maintenance on the boiler to reduce this risk of massive corrosion? Can you get a piping system that creates galvanic problems, perhaps aided by an improper homeowner repair? Is there oxygen drawing into the system due a leaking condensate return line? Are there hard water problems due to the local water supply chemistry?

    Any of the experts have good comments on these problems, or should I start another thread?

    Thanks,
    Rod
  • BobC
    BobC Member Posts: 5,502
    You should start a new thread in the steam section so more people see this.

    Where do you live, some areas are known to have problems with chlorides in the water and that will kill cast iron. Are there any chemicals near the boiler that might be causing a problem? Open containers of bleach, detergents, or rack salt can be a problem.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Fishin_Rod
    Fishin_Rod Member Posts: 31
    Bob,

    Thanks for the advice - I am new to the forum.

    I will start a new thread titled, "Preventing Boiler Corrosion".

    Rod
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,526
    Long day, but she's had her initial skim and is up and running. Too tired for anything more...




    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    RomanGK_26986764589lchmbLionA29Sailah
  • Ironman
    Ironman Member Posts: 7,555
    Nice.

    At first glance, it looked as though the circ and expansion tank were connected to the equalizer. But, I'm 61; it's 9:30 on Friday night. Cut me a little slack. :)

    I hope your gonna replace that POJ CycleGuard with a LWCO that's made for pros. :#
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Gordo
    Gordo Member Posts: 857
    @RI_SteamWorks : Thank you for mounting the VXT the way you did.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • Fishin_Rod
    Fishin_Rod Member Posts: 31
    RI,

    I am new to the forum, but I have already learned a lot.

    For instance, I didn't know you were supposed to leave a guard dog on location for supervision after the initial skim :D .

    Rod
  • gerry gill
    gerry gill Member Posts: 3,078
    what were the chloride levels in this water?
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • New England SteamWorks
    New England SteamWorks Member Posts: 1,526

    what were the chloride levels in this water?

    66.2 ppm.

    Not worried though. Unless and until MegaSteam is proven not to be the antidote to chloride corrosion (and that hasn't happened so far in 10 years) I am assuming the problem is solved. Of course, the usual caveats about water consumption must be scrupulously observed. Having said that though, I am sure there are plenty of MegaSteams out there in the world with leaking vents and an auto feeder without a counter. And still, -no reports of block corrosion.

    Beyond that, the two biggest markers I have observed for early block failure is a Burnham V series or a copper header. These folks had both.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Sailah
    Sailah Member Posts: 826
    And to think all I did yesterday was replace a single vent. install looks great.