Two pipe steam with traps but no condensate return pump.
Mohawk
Member Posts: 2
Came across an old mansion with a seven section HB Smith 350 steam boiler in the basement. So far, from what I have been able to see is that it is two pipe steam with traps on the radiators but no condensate return pump. In my experience a trapped system all ways had a vented condensate receiver. Any thoughts?
0
Comments
-
Say what? Most two pipe systems -- especially vapour systems which I'll be you are dealing with -- do not have condensate return pumps and don't need them. Never did need them. The things are a pain in the neck (and pocket book) and gravity will do all the work for you. Assuming the pressures are correct.
Can you send more descriptions? Any interesting hardware in the vicinity of the boiler? Dry returns? Wet returns? Crossover traps at the ends of the steam mains? Any vents at all (I'd bet on a main vent or group of them where the dry returns end at the boiler)(sometimes these things had no moving parts vents, but were directly vented -- open pipe -- to the chimney or a convenient plumbing waste stack).Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
See if you can find any manufacturers' info, trademarks or other info on any original valves, traps and any odd-looking devices in the piping around the boiler. And take plenty of pics. Post the info here and we should be able to ID this system.
Most two-pipe systems do not need to use a return tank and pump. As Jamie said, they add needless complication and service headaches.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements