Steam Change Out
Dan Foley
Dan Foley Member Posts: 1,268
I looked at this one in Chevy Chase, MD right before Thanksgiving. They don't last very long when they are piped this way.
  • Dan Foley
    Poppy and crew piped in this Crown in early December. This was originally a vapor system that has been bastardized over the years.
    We found the original crossover traps sheet rocked over. Poppy cut holes and replaced them. There was only one bullet vent for the entire system. We replaced with two Gortons.
    The first floor radiators were removed at some point and replaced with Baseray. They run ok at low pressure (12oz).
    ChrisJIronman
  • EzzyT
    EzzyT Member Posts: 1,379
    Beautiful job as always Dan
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875
    Nice work Dan. Are you seeing more commercial work and doing less residential work?
    Again, kudos to the FMC crews.
    ME
  • Nice work Dan, your customer should be well pleased!
    New England SteamWorks
    newenglandsteamworks.com
  • ChrisJ
    ChrisJ Member Posts: 17,104
    It's hard to see in the photos Dan, but why the offset in the flue pipe?
  • Dan Foley
    @ EzzyT. @ RI_Steamworks Thanks!
    @ Mark Eatherton Yes, we are doing more and more commercial work along with larger residential projects with commercial mechanical systems.
    Mark Eatherton
  • Mark Eatherton
    I found that there was better money on commercial. Seems like everyone and their brother is an expert at RFH these days. Unfortunately, none of them knows how to bid the job correctly and they end up being a race to the bottom.
    We had a portable DHW generation system that we'd set up outside the mechanical room to keep the residents in HW while we were switching out the physical plant. One of the Perry boys had some pictures of a mobile unit they'd built a while back. Nice rig.
    ME
    Steamhead Member Posts: 18,272
    This.
    Curious as to why you used a #67 LWCO- is this big enough to require two LWCOs?
    Consulting
  • Dan Foley
    @ ChrisJ Good question. I don't have an answer. I am going there tomorrow to clean and skim so I will take a closer look.
    @ Steamhead I install two LWCO safeties on all of our steam boilers - residential and commercial.
    ChrisJ
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,688
    I can just see you smiling when you got your first look at the Before.
    Superb work, Dan. As always. Thanks for sharing.
    Retired and loving it.
    Dan Foley
  • Abracadabra
    Abracadabra Member Posts: 1,949
    lol @ the original copper equalizer. I thought at first that was the water feeder line into the boiler.
  • Danny Scully
    Danny Scully Member Posts: 1,465
    @Dan Foley I have the answer for @ChrisJ, it's so your installers didn't have to cut a 2" piece of flue pipe. The piece after the offset is a full 24" piece. It's ingenuity at its best!
    Dan Foley
    edited December 2016
    Check this out- the 711C manifold, which hooks up with quick hook-up fittings, and a regular SafeGuard. No moving parts unlike the 67, but you do still have to blow it down:
    http://hydrolevel.com/manifold-fittings/
    Consulting
    SWEI
  • Dan Foley
    @ Steamhead. I use a lot of Hydrolevel products but I was not aware of this one. I will check it out. Thx.
