Has anyone had ignitor errors on their Utica boiler? I have had our contractor service the system twice in the past two months by cleaning the sensors and checking the entire system. They are advising that we replace the ignitor and flame sensors, but they are not 100% sure. Just want to see if anybody has had the same issue and if it got resolved and how. Please let me know. Thanks.
0
Comments
-
Yes. Here are the numbers: Combustion Test for LPGas
128.8 degrees F
5.0 % O2
10.51% CO2
59 ppm CO
90.4% EFF0 -
Have him go through the flow chart in the manual to diagnose it.
What's the flame signal strength @ hi and low fire?
Might also be a bad cable or connection, but he needs to follow the manual to be definitive.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Thanks. The system is less than 5 years old. We never had an issue until this year. I am not sure of the flame signal strength. I will have them contact Utica Tech Support when they arrive to help diagnose properly. Thanks again for your help.0
-
just my opinion but I would have them bring the ignitor/flame sensor with them. If they have never been replaced it wouldnt hurt to be proactive...imho. I usually recommend to my customers to have them done every 3 years... The reading they are looking for is 8 micro amps at 100%. The guide will have them check and answer a number of questions if you still have the manual on hand. If not, I would down load it and keep it on hand for future issues...
0 -
Changing ignitors and sensors every three years seems to be quite often for such a large home system, don't you think? They quoted me close to $500 to do this job. I don't see spending that every three years. I would think with technology nowadays, these things would last longer.0
-
Most of the time, you can just wipe the flame rod clean with a dollar bill; don't use sandpaper. Anything abrasive will ruin it. You could do this yourself without calling a tech.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Ther are new slotted flame sensors that seem to be working better, I've had a few problems with the older style, but only one or two boilers in the first year, could your exhaust be mixing worth your intake air?
Thanks, Bob GagnonTo learn more about this professional, click here to visit their ad in Find A Contractor.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements