Replacing original oil steam boiler, looking for tips

Options
2»

Comments

  • Steamhead
    Steamhead Member Posts: 16,868
    Options
    IIRC, on that type of radiator the top tapping is 1" or maybe 1-1/4". So the boss would be something like 1-3/4" or maybe 2".

    But we'll wait for @drawkcab .
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Eastman
    Eastman Member Posts: 927
    Options
    Whether it's 4.5 or 7 inches, one would be hooking up a 70MBH input boiler for 700 square feet.
  • Steamhead
    Steamhead Member Posts: 16,868
    Options
    Some of that is going to rise into the second floor. The extra boiler capacity can be used for new radiation up there.

    And a steam system is much less likely to freeze in an extended power failure.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • drawkcab
    drawkcab Member Posts: 13
    Options

    The photo of the radiator would surely indicate that it is not 4.5" width, which is the slenderized rad.

    The rad certainly appears to be close to 7" width, which is the standard for the tube type radiator.

    Furthermore, the total EDR of 125 square feet is a bit ridiculous.

    Maybe the OP can measure the width of the rad and confirm.

    Is this the measurement you're asking me to confirm? All the radiators are this size.


    ChrisJ
  • drawkcab
    drawkcab Member Posts: 13
    Options
    Eastman said:

    @drawkcab
    What does radiant mean to you? What would you replace the rads with?

    I incorrectly wrote radiant heat in my earlier post. I meant forced hot water. To me, radiant heat means under the floor or perhaps in the wall but that type/style was not what I was interested in converting to.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,573
    Options
    Steam is going to short cycle and build pressure.
  • Danny Scully
    Danny Scully Member Posts: 1,426
    Options
    Not if he chooses the right boiler @EBEBRATT-Ed
  • ChrisJ
    ChrisJ Member Posts: 15,731
    edited December 2016
    Options
    Smallest Burnham IN is 51,000 output.

    With 28,000 btu/h worth of radiation and a 20% pickup that gives you 34,000 input needed. Even using a big 33% pickup you only need 37,000. A huge, 50% pickup gives 42,000.


    I don't think I'd be happy with any of the steam boilers available. It will short cycle in my opinion.

    If one of them was downfired via removing a burner tube or reducing manifold pressure by someone with a combustion analyzer and training on doing such, it may run beautifully. But in stock configuration the boilers are all way too big. You need to drop 15,000 btu/h +-.



    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Options
    We need to listen to the h.o. objectives more closely. Fact is, here, they find rads are a nuisance.
  • ChrisJ
    ChrisJ Member Posts: 15,731
    Options
    Bob Bona said:

    We need to listen to the h.o. objectives more closely. Fact is, here, they find rads are a nuisance.

    They will find baseboards to be a bigger nuisance because you still need to keep furniture and such away to allow good airflow and there will be more baseboard.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    HatterasguyBob Bona_4
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Options
    The furniture can be closer to the walls where there's a conflict, and other lower profile heat emitter types can be chosen and installed in harmony with the decor.
    ChrisJ
  • SWEI
    SWEI Member Posts: 7,356
    Options
    If you do decide to change them all out, do yourself a favor and stay away from conventional fin-tube. If you absolutely have to have low profile, choose something with a decent radiant output like Runtal UF or Myson Contractor Series.

    Personally, I'd keep the steam.
    Danny Scully
  • drawkcab
    drawkcab Member Posts: 13
    Options
    MilanD said:
    So based on this guide...do these numbers make sense?

    4 tube @ 22" = 4.00
    Number of Sections:
    12 * 4.0 = 48 sqft EDR * 240 BTU = 11,520
    16 * 4.0 = 64 sqft EDR * 240 BTU = 15,360
    8 * 4.0 = 32 sqft EDR * 240 BTU = 7,680
    16 * 4.0 = 64 sqft EDR * 240 BTU = 15,360
    26 * 4.0 = 104 sqft EDR * 240 BTU = 24,960
    Sum radiation heating demand: 74,880 BTUs
  • drawkcab
    drawkcab Member Posts: 13
    Options
    MilanD said:
    So based on this guide...do these numbers make sense?

    4 tube @ 22" = 4.00
    Number of Sections:
    12 * 4.0 = 48 sqft EDR * 240 BTU = 11,520
    16 * 4.0 = 64 sqft EDR * 240 BTU = 15,360
    8 * 4.0 = 32 sqft EDR * 240 BTU = 7,680
    16 * 4.0 = 64 sqft EDR * 240 BTU = 15,360
    26 * 4.0 = 104 sqft EDR * 240 BTU = 24,960
    Sum radiation heating demand: 74,880 BTUs
  • RomanGK_26986764589
    Options
    There was a recent install of a small steam boiler for the townhome with 125 sq feet of EDR. http://forum.heatinghelp.com/discussion/159671/repiping-a-small-columbia-steamer#latest