Contractor installed a wildly oversized condensing boiler

David2NJ
David2NJ Member Posts: 3
I just had a pretty cool condensing boiler installed. It even has a captive indirect hot water tank to get you started. It's a Rinnai QP130N. It's an old house but only 1650 s.f. and well insulated. It does heat the house and the hot water just fine. But I think I needed something about half that size. Why he didn't recommend the smaller QP85N or some other unit is beyond me. Now I have to pay for all that extra gas which obviates the savings of going to a condensing unit in the first place. Argh!!!!!

Comments

  • JohnNY
    JohnNY Member Posts: 3,294
    Considering the 5:1 turndown ratio, the minimum input on the 85 is 17MBH, while on the 130 it's 26MBH. It's not much different. Contractor probably wanted to make sure you get enough hot water.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • njtommy
    njtommy Member Posts: 1,105
    Paying for extra gas is one problem. The biggest problem that Will kill your boiler is short cycling. Is the house all 1 zone or does it have multiple zones?
  • kcopp
    kcopp Member Posts: 4,472
    Did you ask him? Id he made a mistake he should make right and fix it?
  • hot_rod
    hot_rod Member Posts: 23,407
    If the boiler provides heat and DHW that is about as small as you can go or DHW will be inadequate.

    How cold is your incoming water in winter?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Zman
    Zman Member Posts: 7,611
    I would not describe your system as "wildly oversized"
    With combi systems, it is common for the boiler to be over sized for the heating load. It is just the nature of combi's.

    Since the combi has some internal storage, you may well have been able to get by with the smaller unit. In hindsight, the installer should have asked more questions about your preferences. It sounds like you would have been OK occasionally running out of hot water in exchange for a more efficiently sized system.

    How long is your typical heating cycle?
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein