Contractor installed a wildly oversized condensing boiler
David2NJ
Member Posts: 3
in Gas Heating
I just had a pretty cool condensing boiler installed. It even has a captive indirect hot water tank to get you started. It's a Rinnai QP130N. It's an old house but only 1650 s.f. and well insulated. It does heat the house and the hot water just fine. But I think I needed something about half that size. Why he didn't recommend the smaller QP85N or some other unit is beyond me. Now I have to pay for all that extra gas which obviates the savings of going to a condensing unit in the first place. Argh!!!!!
0
Comments
-
Considering the 5:1 turndown ratio, the minimum input on the 85 is 17MBH, while on the 130 it's 26MBH. It's not much different. Contractor probably wanted to make sure you get enough hot water.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Paying for extra gas is one problem. The biggest problem that Will kill your boiler is short cycling. Is the house all 1 zone or does it have multiple zones?0
-
Did you ask him? Id he made a mistake he should make right and fix it?0
-
If the boiler provides heat and DHW that is about as small as you can go or DHW will be inadequate.
How cold is your incoming water in winter?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I would not describe your system as "wildly oversized"
With combi systems, it is common for the boiler to be over sized for the heating load. It is just the nature of combi's.
Since the combi has some internal storage, you may well have been able to get by with the smaller unit. In hindsight, the installer should have asked more questions about your preferences. It sounds like you would have been OK occasionally running out of hot water in exchange for a more efficiently sized system.
How long is your typical heating cycle?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements