False Pressure Release Time?

kredmore
Member Posts: 53
I have an average size two pipe home vacuum low pressure system that is well maintained, and have learned quite a bit here and over the years. There is false pressure after the heating cycle has been satisfied. Two questions that I couldn't find info upon searching, as I think I noticed higher than normal false pressure:
1) How long should it take for the False Pressure release to return to zero? Estimated -15 lbs to 0. Meaning, is it being release fast enough, via Hoffman 76? Two Main vents - Hoffman 75s.
2) Is this high (if it's high) false pressure harmful to a system?
Hopefully, this is enough info, but can certainly provide more as needed.
Thanks, Keith
1) How long should it take for the False Pressure release to return to zero? Estimated -15 lbs to 0. Meaning, is it being release fast enough, via Hoffman 76? Two Main vents - Hoffman 75s.
2) Is this high (if it's high) false pressure harmful to a system?
Hopefully, this is enough info, but can certainly provide more as needed.
Thanks, Keith
0
Comments
-
I'm not quite sure I know what you mean by "false pressure". Do you mean a vacuum which the system drops into after it has fired? Or that the pressure stays up after the system quits? Or what?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch0 -
negative pressure that the system drops into after heating cycle is satisfied.0
-
That's referred to as a vacuum. I suspect that you are referring to 15 inches of water vacuum, not 15 psi -- which would be extraordinary.
The longer it sits there, the better -- that simply means that the system is nice and tight and extracting more from the residual heat in the boiler.
It's a very good thing...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch1 -
ok, thanks. sounds like all is good!0
Categories
- 81.2K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 37 Biomass
- 394 Carbon Monoxide Awareness
- 2.7K Controls
- 1.4K Domestic Hot Water
- 3.8K Gas Heating
- 101 Geothermal
- 133 Indoor-Air Quality
- 2.4K Oil Heating
- 32 Pipe Deterioration
- 581 Plumbing
- 4.3K Radiant Heating
- 334 Solar
- 12.3K Strictly Steam
- 38 Water Quality
- 11 Industry Classes
- 53 Job Opportunities
- 8 Recall Announcements