Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Radiant heat, modulating boilers & constant circulation questions

doooglasss
doooglasss Member Posts: 18
edited December 2016 in Gas Heating
I have homeowner/DIY designed a radiant heat install for my home. I utilized LoopCAD for the design and heat loss calculations. My plan is to convert from baseboards & oil heat to gas heat and constant circulation radiant with outdoor reset to control inside temperature.

My LoopCAD drawing claims a required heat output of 31 k btu. I have an ~1,800 sq/ft ranch- above ground floor is 1k sq/ft and partial below ground (walkout) is 850 + garage. I am in the process of renovating 75% of the home so I am trying to air seal it (closed cell spray foam) and provide proper insulation to make this the most efficient install as I can get it to be.

Currently I have Uponor 1/2" HE-PEX installed with a suspended pipe design using clips (more below).

Products I have purchased:
-Tekmar 360 Control with outdoor & indoor sensors
-Uponor EP manifold- 10 ports total
-Thin metal 4 ft. eBay heat spreader plates (4" wide), about 400 of them
-Grundfos 15-55F pump

Pictures of my piping design & control strategy are below.

I have a few questions:

1. I was told that doing the thin heat plates would be superior to a suspended tube design. Is this correct?

2. LoopCAD tells me that I should use 3/4" pipe to supply the manifolds due to an estimated flow of 3 GPM. If I make the radiant heat system the primary boiler loop is restriction of flow bad for the boiler? If I change to 1" or 1.25" primary piping is the lack of pressure bad for the manifolds? Maybe the solution is to make a 3/4" bypass with ball valve?

3. My control concept is to have the Boiler ODR determine the temperature of water to produce and the Tekmar to determine the calls for heat and fire the boiler based off feedback from the indoor sensors. Also this will prevent the boiler from short cycling (I believe?). Can I just jump the thermostat terminals on the Tekmar or should I connect them to my Nest Thermostat and use it as a high heat cutoff by setting it to say 75 when my Tekmar indoor desired temp is 70?

4. Recommendations on boilers? My plumber had me leaning towards a Navien unit and I would do a separate wall mounted on-demand water heater too. I've also looked into Bosch gas burners recently too.

5. Is a fully modulating boiler built to run 24/7 without input from my Tekmar or a thermostat but just operating off of an ODR control? I feel like this would be the simplest setup?


image

image
vincyking11212

Comments

  • Gordy
    Gordy Member Posts: 9,546
    An "extruded"plate under floor design will out perform a suspended tube. However plated over the top is even better..not thin plates.

    Be aware of floor covering r values which will reduce output, and response time of the panel.

    Most mod/ cons come with onboard controls. Some can have up to 3 different temp zones plus DHW priority. So pay close attention to your boiler selections capabilities out of the box. Think carefully about control needs not price.

  • Gordy
    Gordy Member Posts: 9,546
    When you select the right boiler based on heat loss, and control strategy. Follow the boilers manufactures piping diagram.

    3/4" copper pipe will deliver 45 kbtu at 2-4 fps
    1" 72kbtu
    1 1/4" 145k
    1 1/2" 225k
  • Brewbeer
    Brewbeer Member Posts: 616
    Why would you use a dedicated on-demand water heater for domestic hot water, instead of an indirect tank fired by the boiler?

    31,000 btu heat loss indicates a small boiler is in order. NHB-55?
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
    Gordy
  • Gordy
    Gordy Member Posts: 9,546
    Missed the tankless... agree with @Brewbeer
  • Zman
    Zman Member Posts: 7,561
    I agree with the above recommendations.

    I am not sure why you are considering a mixing controller for a modulating, condensing boiler. It is more efficient and simpler to just modulate the boiler to the target temp.
    Tekmar has other products that will handle that if the boiler you choose does not have the capability.

    Your question about pipe sizing will be partially dictated by the boiler selection.


    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • doooglasss
    doooglasss Member Posts: 18
    edited December 2016
    Thank you for all the replies! I'll do my best to respond, but it seems that this all comes down to boiler selection (controls, piping and DHW). Could you guys recommend a few NG boilers that would work for my situation?
    Brewbeer said:

    Why would you use a dedicated on-demand water heater for domestic hot water, instead of an indirect tank fired by the boiler?

    At first I was looking at a Navien combi-boiler, but learned that they do not modulate as low as the dedicated Navien boilers.

    Opting for on demand instead of tank is really an issue of space. Why would a tank be preferred over a on-demand heater that can provide adequate temp raise & flow?
    Gordy said:

    An "extruded"plate under floor design will out perform a suspended tube. However plated over the top is even better..not thin plates.

    Are you saying thin plates will be LESS effective than suspended tube? My understanding from my reading online tests and the ASME study on heat transfer plates was (best to worst):

    tube in slab > warmboard style subfloor panels > extrude underfloor plates > thin underfloor plates > suspended tube > staple up
    Zman said:


    I am not sure why you are considering a mixing controller for a modulating, condensing boiler. It is more efficient and simpler to just modulate the boiler to the target temp.
    Tekmar has other products that will handle that if the boiler you choose does not have the capability.

    I was not planning on utilizing the mixing portion of the controller. The control was really purchased to prevent short cycling and the indoor feedback feature for the ODR curve. I only purchased the 360 > the 260 because I got a great deal on a new old stock unit ($200).

    I purchased this secondary control (instead of only utilizing the Navien's onboard ODR) because I was told by Navien's tech support that jumping the boiler thermostat terminals (instead of connecting a thermostat) would result in the boiler short cycling itself and I needed a control that would prevent that.

    I had assumed the Navien ODR would modulate the boiler and the Tekmar would attempt to provide heat demand for the house (taking the place of a thermostat). Am I over complicating this and should just connect my Nest?
  • Zman
    Zman Member Posts: 7,561
    The 360 is a mixing controller. It is also capable of basic on/off boiler control. I don't see how you will integrate it with a modulating boiler.

    I would suggest looking into the firetube designed boilers like triangle tube, lochinvar whn and others. I would not consider anything other than a stainless heat exchanger.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Solid_Fuel_Man
  • Brewbeer
    Brewbeer Member Posts: 616


    At first I was looking at a Navien combi-boiler, but learned that they do not modulate as low as the dedicated Navien boilers.

    Opting for on demand instead of tank is really an issue of space. Why would a tank be preferred over a on-demand heater that can provide adequate temp raise & flow?

    An indirect tank doesn't require separate gas line or separate venting, doesn't require regular annual maintenance, doesn't have sensitive moving parts to fail, and will have better high and low flow rate performance.

    And here is the video: https://youtube.com/watch?v=vffdymvjluk
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
    doooglasss
  • Gordy
    Gordy Member Posts: 9,546
    I always shudder when I hear light weight plates.

    If you are going Mod/con the goal is designing an emitter system that uses the lowest awt possible. This promotes more time in condensing mode which takes you from upper 80's efficiency to mid 90s. Suspended tube, or staple up is a bad choice to achieve this. Will they heat the space? Yes, but at a hit to efficiency. You have a clean chalk board use it well.
  • doooglasss
    doooglasss Member Posts: 18
    Gordy said:

    I always shudder when I hear light weight plates.

    If you are going Mod/con the goal is designing an emitter system that uses the lowest awt possible. This promotes more time in condensing mode which takes you from upper 80's efficiency to mid 90s. Suspended tube, or staple up is a bad choice to achieve this. Will they heat the space? Yes, but at a hit to efficiency. You have a clean chalk board use it well.

    My issue is cost. The extrude plates are substantially more money (~$2,800 vs ~$500 I spent).

    Do the thin plates work better than a suspended tube design?
  • hot_rod
    hot_rod Member Posts: 22,024

    Gordy said:

    I always shudder when I hear light weight plates.

    If you are going Mod/con the goal is designing an emitter system that uses the lowest awt possible. This promotes more time in condensing mode which takes you from upper 80's efficiency to mid 90s. Suspended tube, or staple up is a bad choice to achieve this. Will they heat the space? Yes, but at a hit to efficiency. You have a clean chalk board use it well.

    My issue is cost. The extrude plates are substantially more money (~$2,800 vs ~$500 I spent).

    Do the thin plates work better than a suspended tube design?
    First, define light weight?

    There were some made with thin flashing gauge material, forget those. They would make all sorts of noise when the heat hit them and poor heat transfer from tube to aluminum.

    There is also a "lite" version of the popular, and original ThermoFin out of Bozeman, called ThinFin C. ThinFin is 3.5" wide instead of 4" and a .050 compared to .0625.

    But the thick extrusion at the tube is the key to a quality transfer plate, that is the same on both.

    I suspect most of the radiant companies buy that product.









    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Gordy
  • Gordy
    Gordy Member Posts: 9,546
    A plated install works better yes. However as @hot rod mentioned the key is how well the plate fits the tube, and how well it fits to the underside of the floor. Thin plates promote noise.

    Conduction is king. Water to the tube, tube to the plate, and plate to the floor. Any gaps in that chain decrease output, and efficiency.

  • hot_rod
    hot_rod Member Posts: 22,024
    Here is what it looks like

    Suspended tube, old Wirsbo method

    Wirsbo in ThermoFin, even the screws become heat transfer mechanism :)


    The last pic shows from closest
    Warmboard

    ThermoFin with copper tube, notice where tube is pulled from slot to make connections

    Wirsbo in ThermoFin

    Suspended tube

    Staple up rubber Onix (with heat transfer staples

    The left hand side of each has berber carpet, no pad . Same supply temperature, same flow rate.




    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    It looks like the onix is the best at transferring heat to the plates. What are the 5 different types in the first picture? All wirsbo?

    Taylor
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • hot_rod
    hot_rod Member Posts: 22,024
    Copper in plates was the best output. Warm board was great also, but 12" OC shows some striping. Floor covering helps smooth out some stripping.

    Notice on the Warmboard where I roistered through the aluminum. It cuts the heat transfer right out.

    Suspended and staple up Onix were the bottom two performers.

    With staple up Onix, the staples become the best transfer "medium".

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mark Eatherton
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,853
    HR, mind if I borrow those photos for educational purposes? VERY graphic.

    Thanks for all you do for our industry.

    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • Eastman
    Eastman Member Posts: 927
    Regarding the boiler controls:

    I think you are over complicating this. As far as I know, the Tekmar 360 can't modulate a boiler. The boiler would still rely on its internal target setpoint to adjust the firing rate. The boiler target and the tekmar target would generally not be in sync and this would be counterproductive to the efficiency of the system.
  • hot_rod
    hot_rod Member Posts: 22,024

    HR, mind if I borrow those photos for educational purposes? VERY graphic.

    Thanks for all you do for our industry.

    ME

    Sure, the RPA helped fund that project.

    I have close up of the individual panels also. I'll find the original disc for best clarity.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Oh, I was confused as to which was which. Was that soft copper in extruded aluminum plates for the winner?
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • hot_rod
    hot_rod Member Posts: 22,024
    It was rigid type M copper. I crimped pex on the ends to make the connections to the manifold. You can see where I pulled the copper out of the groove a small amount to make the crimp connection. Once tight tube to aluminum conduction is compromised, the heat transfer goes away quickly.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream