Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Comfort maker furnace

I have a comfort maker furnace that has a bad circuit board, mod.#1014460, that board is discontinued and the replacement Honeywell universal board is mod.#ST9120U1011. I'm not understanding the instructions, and as to which harness to use. It saids to disconnect the 9 pin molex plug and plug into harness ST9101, the old board doesn't have a 9 pin connector, it only has a 6 pin connector. Confused, can anyone help...

Comments

  • Tim McElwain
    Tim McElwain Member Posts: 4,641
    The instructions cross reference should tell you which harness to use. You should plug the harness into ST9120U1011 six pin connector and the plug from the old control into the harness. I do not have my instruction for that control handy it is at my training center. If you can wait until tomorrow I can check it.