Help needed w/heat loss calculation...
john p_2
Member Posts: 367
in Gas Heating
Trying to help a friend out and myself to understand heat loss a little better, maybe someone can shed some light on this for me.
Did a calculation on the US Boiler Company website and all results posted below but I don't understand...what/why is a range of temperatures given?
And by the way this calculation was being done for a possible garage unit heater in a 30' X 30' & 8' ceilings w/6" insulation
Total Heat Loss for 60 F Temp. Diff. = 31,209.00
Total Heat Loss for 70 F Temp. Diff. = 36,826.62
Total Heat Loss for 80 F Temp. Diff. = 41,820.06
Total Heat Loss for 90 F Temp. Diff. = 46,813.50
Total Heat Loss for 100 F Temp. Diff. = 51,806.94
Did a calculation on the US Boiler Company website and all results posted below but I don't understand...what/why is a range of temperatures given?
And by the way this calculation was being done for a possible garage unit heater in a 30' X 30' & 8' ceilings w/6" insulation
Total Heat Loss for 60 F Temp. Diff. = 31,209.00
Total Heat Loss for 70 F Temp. Diff. = 36,826.62
Total Heat Loss for 80 F Temp. Diff. = 41,820.06
Total Heat Loss for 90 F Temp. Diff. = 46,813.50
Total Heat Loss for 100 F Temp. Diff. = 51,806.94
0
Comments
-
Different areas of the country have differed design temperatures (minimum expected).
The temperature difference is between desired room temperature ( 70 degrees for a house) and the expected minimum temperature for your area (in my area it's 5 degrees).
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thanks so much Bob0
-
Your welcome. Don't ever be afraid to ask a question - someone on the forum will have an answer.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
36,826 btus = almost 41 btus per sq. ft. That sounds awful high.
I would recommend that you down load SlantFin's heat loss app and use that. It will be a lot more accurate.
Online calculators will grossly over-size.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I actually have the SlantFin & Taco's but found the US Boiler one and thought it might be a little easier for my friend to use and see for himself what kind of things go into a heat loss calculation.
It is a garage on grade with uninsulated walls and two large garage doors.0 -
Formula: Heat Loss Through a Building Component = U-Factor x delta T x Area
U factor is reverse on R factor. R Factor is cumulative of the thermal resistance of every component of the wall - sheeting, insulation, sheetrock or other interior finish. Add the R values for all of them. Then reverse as a fraction. For example if total R value is 18, then U value is 1/18. If R=25, then U=1/25.
Delta T is the difference between the temperature outside and the temperature you want to maintain inside. Usually 65 F is used as a standard for indoor temperature. So if it is 20F out, delta T = 65-20=45. This is why the calculator you used gave you multiple options.
Area - calculate all external walls and possibly ceiling. If the garage is detached (all walls and ceiling are external), then your area is 4 walls 30x8 + ceiling 30x30. If the garage is attached to a house, only 3 walls and a ceiling will be external. If the garage is part of the house, then only one wall is external.
The number you get is your heat loss measured in BTU/hour. This is conductive heat loss through materials. Convective heat loss (through holes and gaps) is separate formula.
Kind of late response, but I just recently found this forum. Maybe it will help somebody in the future.1 -
Maybe there is someone in your area that knows how to do such things .
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements