PRV placement on closed heat exchanger circuit?
For my new heating system I have my heating zones on a closed circuit drawing heat from coil heat exchangers in my buffer tank. Been trying to determine the best location for the PRV. I was thinking right at the begining of the supply from the HXs? or tee'd off from the expansion tank line between the Air separator and expansion tank? Also between those two will be my make up water with feed valve.
0
Comments
-
PRV can mean one of two items. One is pressure reducing valve. If its that, then it needs to be connected to the expansion tank connection serving the system. If its pressure relief valve, then it should be connected to the outlet side of the load side of the HXer serving the system.
Which PRV are you referring to?
METhere was an error rendering this rich post.
0 -