Customer has had no issues with this unit until about a month ago. Since then it has a new Genisys control, cad cell, electrodes, igniter, and nozzle. Pump psi is good, ohms are normal on eye. All combustion readings are normal. It has a tiger loop so air is not an issue. It will not stay running. Go there everytime and hit the reset and it lights right up perfect, no smoke, no delay, nothing...turn it on and off several times with no problem. Leave the house and a day or two later it's out. What is going on here? Anybody had an issue like this before?
We are going to need more info .... combustion test readings...draft over fire and at breech....pump pressure....vacuum...etc etc....somethings going on there...ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Does have a delay valve, have not looked for dead spot on motor. Thank you for that, I will be trying that next. Genisys history just says "did not light" run times are consistent with pre purge plus lockout everytime ...not very helpful when it won't reproduce the issue while I'm in front of it. Might be dead spot....Customer said cable company was there a month ago "messing with wiring in house"0
Is there a combustion air issue?
I don't think it has a combustion air issue, it's in a hallway and has never had an issue in years until now. Nothing obstructing it
Combustion readings were 11 co2 -.05 breech -.01 over fire.....the burner is set to spec, 60 80 a at 145.....it's not in tuning because I checked and rechecked the basics myself0 -
Also, check the pump coupler.
Rick0 -
Echo the motor possible, and add delayed oil valve and bad pump possibly into the mix0
Had this happen twice . Did all that you said, changed parts I'd go hit reset run then off on safety I read history on Genysis Recycle was on contractor tool. Called Beckett seems Miller Puts a pad on Motor covers air inlet motor over heats goes off you go hit reset it will run a day or two0