Minimum safe hot water boiler water return temperature
BruceLundeen
Member Posts: 7
During these so-called shoulder seasons sometimes spaces are overheated even with 140 degree return temperature. Much has been said about condensation ruining non-ModCon boilers when running lower water return temperature.
You know, it is very brief periods that the reset controller will hold the water temperature this low.
Anybody have any first hand experience - especially bad experiences (like a failed boiler)?
You know, it is very brief periods that the reset controller will hold the water temperature this low.
Anybody have any first hand experience - especially bad experiences (like a failed boiler)?
0
Comments
-
Most all Mod/con boilers have no issue at all w/ low temp return water temps because of their construction... they love low temp water.
Now a typical cast iron boiler that's different. The low water temps can do 2 things... shock the boiler if a cold slug returns to a hot block AND prolonged temps will allow condensation to form on the fire side to become acidic. That will eat through the cast over time.0 -
Buffer tank. Let the boiler keep the buffer tank up to temperature -- it won't have to run that often in the warmer weather -- and run your system with another pump and mixing valve using the buffer tank.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
It sounds like you have an outdoor weather responsive control on this boiler. I would check the reset curve. It's programming may be off a little. Depending upon the unit there are several factors needed to calculate the proper curve like:
1. Outside Design temp (different than the coldest it has ever gotten)
2. Minimum Supply water temp
3. Maximum Supply water temp
4. Warm weather shutdown temp
Dave HDave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -
Here's what can happen when you don't protect the boiler from low water return temps.
New customer, claims it was cleaned last year. Could've been. This is what Icesailor used to call 'Kibbles & Bits'
There was an error rendering this rich post.
0 -
did you salvage / clean that mess?
or replace it?
wow, just wow,known to beat dead horses0 -
Cleaned it, and it runs fine-2 vacuum full bags later. Inside the chamber you can see where the crud was as high as the bottom of the air tube. Have to go back to install bypass (boiler protection).
There was an error rendering this rich post.
0 -
surprised to see it that bad on a steel boiler w a tankless. The circulator would usually turn off until the boiler got back up to temp.0
-
I agree. Install a boiler bypass which will let supply boiler water mix with cooler return water to raise the boiler return water temp.0
-
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements