I have a single pipe steam system and am interested in installing the Baseray in my home.
I am trying to find out if it is compatible with a single pipe system.
I am trying to find out if it is compatible with a single pipe system.
0
Comments
-
You have to pipe the baseboard in using two pipes. The supply feeds into the top tapping on one side. The return leaves the opposite bottom tapping. The return line then runs down to the floor of the basement where it then does a 180° turn back up. This return then has to enter back into the main steam line into a tee fitting (you have to add into the main) facing down.
What will happen, the return loop (at least 5' tall) will fill with condensate and prevent steam from entering the baseboard backwards. the condensate will leave the baseboard through this return line and enter the steam main at the bottom facing tee where it joins condensate in the main and returns back to the boiler. There is a write up in the Lost Art of Steam Heating book by Dan regarding it.
You can do it and it will work well. If you only adding in a small section of BB like a 3 or 4 section you can probably get away with only one pipe, but long runs have to be piped two pipe .0 -
Thank you Eric.
I will be installing a 6' section so it sounds like it should work.0 -
Eric - curious which chapter of LAOS covers this install? Do you happen to have a field pic of the install you describe? I have two 10ft baseray's installed on a second floor. No way I can add that much pipe at this point but still curious nonetheless. I do feel I could connect the supply of the steam on the top trappings as opposed to the bottom, which they are connected to currently.0
-
I keep toying with the idea of installing about 6' myself. I have a 6' wide bay window that currently has a double 2" fin-tube convector that never heats all the way accross (the EDR is way out of line) and doesn't stay warm very long between cycles. What I'd really like is a short, two-column window radiator, but they're really hard to come by. The Baseray looks like it would do the job, but the install isn't going to be easy, so I'm interested in hearing how well this works if you go ahead with it..Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
I generally try to steer people away from cast iron baseboard with 1-pipe steam and toward cast iron convectors:
http://www.governaleindustries.com/products/convectors/Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
John - I might replace my two 10ft baseray and curious what's your field exp with the convectors? They can be mounted or can be seated on the floor. If exposed I would have to build a nice cabinet with perhaps openings for a grate/mesh. I notice the longest unit they have is 5ft. I'd imagine this is the sweet spot for a 3/4 one-pipe steam application. Curious how big of a room these can serve.0
-
I looked at that PDF and they don't tell you the EDR of the convectors, is there another pub that covers this?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
You can find the BASERAY inst. manual on line. Burnham recommends 2 pipe steam only or for one pipe use the method @Eric mentioned above from Dan's book. I would not do a one pipe connection , it is sure to hammer loudly0
-
Can these be piped as single pipe ( with no drip ) ?JohnNY said:I generally try to steer people away from cast iron baseboard with 1-pipe steam and toward cast iron convectors:
http://www.governaleindustries.com/products/convectors/
hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
0 -
@hvacfreak2 You can pipe it single, however you might have problems with spitting air vents and or water hammer.hvacfreak2 said:
Can these be piped as single pipe ( with no drip ) ?JohnNY said:I generally try to steer people away from cast iron baseboard with 1-pipe steam and toward cast iron convectors:
http://www.governaleindustries.com/products/convectors/
I just did a job and the owner had it installed in three rooms, the living room had two of them about 10' ea so did the dining room. Also an upstairs bedroom had a 10'er they all have a rigged venting apparatus on the end using 1/4" tube with compression fittings and a 1/8 tee that the air vent is connected to centered between the top and bottom tapping. Unbelievably they work quietly evenly and don't spit.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
saw a thread in here that mentioned convectors should are configured for a 2 cycle system and I believe most single-pipe systems are recommended to be running on 1 cycle. Any issues with that setup?0
-
That's an amazing little setup Dave. Do you think copper was used for flexibility in that space ? I wonder the reasoning that lead to creating this "hack". Seems clever.0
-
I have 1929 single-pipe gas-fired steam heat. I replaced two of my old radiators with 6' cast iron (Baseray?) basaeboard units. They are mounted on the wall to get the proper pitch and the air vents are on little copper pipe extensions so they are high enough not to spit. They work great.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements