Weil Mclain 230 boiler shutoff due to outdoor sensor - help!
bythecshore
Member Posts: 6
I am a non-professional, just a guy trying to fix my boiler. It stopped working this morning. The display (see photo) says its the outdoor sensor. Can I disconnect that temporarily to get it working? It's Sunday and the HVAC company is closed...
Thanks!
Thanks!
0
Comments
-
Here's the manual if you don't have it:
http://www.weil-mclain.com/sites/default/files/field-file/ultra-series-3-manual_1.pdf
Did you try manually reset?
I didn't read thru the manual but you may be able to either:
1. Put it in test mode.
2. Remove outdoor reset. I didn't read into it enough to see if you can do that via programming and/or you have to remove the wires for the outdoor sensor from the control.
Also, there is a safety recall on that unit:
http://www.weil-mclain.com/ultra-gas-recallThere was an error rendering this rich post.
0 -
Thanks for the manual.
I did try the reset, which got rid of the lockout. But it's "stuck" on standby because of the outdoor sensor issue.
I know there the two wires are screwed onto the circuit block, but I don't know where that is. I took off the cover (photo attached) but still don't see it. Assuming I can find it, do you think removing the wires will fix it?
0 -
Find the sensor outside.
Pull one of the wires off the sensor.
You will need a very small screwdriver.
I'm guessing the sensor got wet and is trashed.
0 -
-
OK, that worked, thanks!! The heat is back on! My wife says thanks too.
Do i need to replace the outdoor sensor? It's an optional device according to the manual. What does it do, anyway?0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements