Weil mclain gv90
Paul_69
Member Posts: 251
in Gas Heating
What are some things to look for when thermal fuse failed . Inducer started and ran ok and vent seems clear
0
Comments
-
If the inducer is running then I would check the pressure switch. Actually need a little more information from you.0
-
Why pressure switch? I was not there.another tech was. I will be going once I have switch to get unit to run again. Can u give me some check points. Thx0
-
Check the differential pressures to see what the draft is running at. Check the length of run on the venting, are you near the edge of it's limit. Check gas pressure's to see if the unit is over fired. Check the burner's for damage, warping or cracking and alignment...Is the unit piped direct vent and if so is it clear...if not is there enough combustion air...1
-
This boiler might have the HSI that doubles as a flame sensor.
As it ages it might still be a good HSI, but drops the ball as a flamer sensor. After the inducer fan proves it is next in line for ignition, which it may do. But not work as a flame sensor, fire and drop out and repeat.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements