quick question
Paul S_3
Member Posts: 1,261
im installing (2) Williamson gwa 50's with an output of 38k.. for each apartment....heat loss is about 33k at 0F....i would like to protect boilers with a 1/2 line in front of pump to return with globe valve in line.....what woukd you guys do "real world" BPvalve isnt in budget either is iseries....thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
What type of heat emitters. It's rare to need protection with fin tube or any low mass types. Cast iron rads?
The only absolute means of providing return protection is with a devise that can detect and respond to temperature. Bypass valves or pumps, they just guessBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
one system CI bsbd...other CI radsASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Heat emitters already installed? If the emitters can dissipate the heat energy faster that the boiler provides it, you have the potential to run below dew point.
The thermal mass and volume of system fluid would factor in also.
The two ball valve balance method is only good for the single condition you set it for, above or beyond either it doesn't protect, or bypasses more than needed.
There is always the "poor mans method"
Some of the basic Viessmann cast iron boilers had an additional aqustat that turned off the pump when the boiler dropped into the low return temperature conditions. A simple, somewhat crude, bang-bang method of protection.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements