Radiator valves and system identification

mak62
mak62 Member Posts: 11
Saw these on a unrelated service call





Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,525
    Broomell system, or it was... once upon a time... @Steamhead knows all about them; I don't, but as I recall they are discussed in the Lost Art, and they are a vapour system.

    That near boiler piping is... um... unfortunate.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    RomanGK_26986764589
  • KC_Jones
    KC_Jones Member Posts: 5,796


    That near boiler piping is... um... unfortunate.

    Someone certainly needs directed to the manual that's for sure. Yuck.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • mak62
    mak62 Member Posts: 11
    Yes near boiler piping a mess, couldn't see or find any vents.
  • Steamhead
    Steamhead Member Posts: 17,314
    edited October 2016
    Jamie nailed it.

    The Broomell system would have had a cast-iron "condensing radiator" hanging from the ceiling near the boiler. The dry returns routed air into one end of this, and the other end connected to the chimney. The chimney draft helped pull air from the system.

    I worked on a VECO system once that had a similar setup when it was installed. Some knucklehead had screwed up the piping so the air couldn't vent, and the system did not heat well. Once it was fixed, everything heated great.

    This system appears in chapter 15 of Dan's book "The Lost Art of Steam Heating".
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mak62
    mak62 Member Posts: 11
    Thanks for all your help
  • gerry gill
    gerry gill Member Posts: 3,078
    Near boiler piping could use some work...bet the installer of the insulation was proud of that job too...lol
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.